Liquid line increase
Hi
While looking at large cold room with 3 blowers supplied from 3 carrier condensing units,I noticed the liquid lines went from 5/8 to 7/8 about .5 meter after sight glass.Is this ok.
Regards Bernard
-
27-07-2006, 08:55 PM #2
Re: Liquid line increase
I dont see any reason why not. a system with an excessively long pipe run could have the tubing oversized to compensate for any pressure drop involved.
Takes a licking, keeps on ticking.
-
27-07-2006, 09:05 PM #3
Re: Liquid line increase
Hi Bernard,
I doubt the difference in sizes will present any problems. When I did a lot of supermarket work I routinely over sized the liquid lines, and insulated them in areas where the piping ran through a warm space.
The larger piping allows a lower pressure loss in the liquid line. That helps a lot. Secondly, if the liquid line runs through a space with an air temperature lower than the liquid line temperature, that also helps.
If the liquid line runs through a warm space, the liquid line can absorb heat, which does not help you. In fact, it can decrease the system capacity.
-
27-07-2006, 10:24 PM #4
Re: Liquid line increase
Hi
Yes the pipe runs are long so thats the reason,another question the condensers were large but the recievers small.You would never be able to pump them down.Sorry I don,t have much info on the system and they were running fine.But should the receivers not be sized to cope with the liquid in the system.
Thanks Bernard
-
27-07-2006, 11:52 PM #5
Re: Liquid line increase
Originally Posted by bernard
I would question why the receiver is so small, unless it was intended for a close coupled system.
Similar Threads
-
Suction gas <-> liquid line heat exchange and performance gains
By DaBit in forum Technical SpeculationsReplies: 30Last Post: 18-05-2010, 01:52 PM -
liquid line sight glass mystery
By austech in forum Technical DiscussionsReplies: 19Last Post: 18-07-2006, 08:16 PM -
Liquid line for multi evaporators
By Kevin Yeo in forum Supermarket RefrigerationReplies: 1Last Post: 29-12-2005, 02:29 PM -
Parker levels in ammonia systems
By Friobernal in forum IndustrialReplies: 3Last Post: 04-08-2005, 03:46 PM