    Carrier Conversions



    I've been asked to convert 3 x 70kw Carrier air cooled DX condensing units from R22 in preparation for the phase out of R22.

    The units are single stage 6 cylinder semi - hermetic compressors (76A flc) with no unloaders. They appear to be recon compressors and operating quite satisfactorily.

    Which gas should I choose?

    It's an air conditioning application presently evaporating at 5C.




  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Carrier Conversions

    A little bit here Frank by someone else regarding a chiller gas change might be of interest.
    http://www.modbs.co.uk/news/fullstor...ler_life_.html

    plus this item from earlier...
    http://www.refrigeration-engineer.co...hp/t-1727.html
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Carrier Conversions

    Thanks Brian - I was considering R59 but I've heard bad reports of oil recovery.

  4. #4
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Thumbs up Re: Carrier Conversions

    R407c and you can keep TEV.

    Renato

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Carrier Conversions

    Quote Originally Posted by Renato RR
    R407c and you can keep TEV.

    Renato
    There may be a residual oil problem with 407C

  6. #6
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Thumbs up Re: Carrier Conversions

    Well you will nedd change it 4-5 times before becomes ok.Cut off all sifons and empty old oil from traps.

    Renato

  7. #7
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Carrier Conversions

    Quote Originally Posted by frank
    I've been asked to convert 3 x 70kw Carrier air cooled DX condensing units from R22 in preparation for the phase out of R22.

    The units are single stage 6 cylinder semi - hermetic compressors (76A flc) with no unloaders. They appear to be recon compressors and operating quite satisfactorily.

    Which gas should I choose?

    It's an air conditioning application presently evaporating at 5C.

    In a case such as this a phased change is better. First change the oil to ester oil, keep the R22 and keep changing the oil until the lab tells you the mineral oil % is below 1 to 3% (your oil manufacturer will help you with this figure).

    When the oil is flushed, then it is time to change to the new refrigerant, probably R407c, even though I don't like it, it is probably the only alternative atthe moment.

    Hope this helps.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  8. #8
    Join Date
    Mar 2006
    Location
    Philippines
    Age
    53
    Posts
    124
    Rep Power
    19

    Re: Carrier Conversions

    Hi,
    I used r407c for replacement of r22. No problem yet.

  9. #9
    Join Date
    Feb 2006
    Location
    UK
    Posts
    16
    Rep Power
    0

    Re: Carrier Conversions

    Conversion from R22 to a HFC such as R407c is frought with problems, and could be a very costly exercise.

    Du Pont now offer the Isceon range and we have found Isceon 59 (R417a) excellent as a 'Drop In for R22 on DX systems.

    This gas is not cheap and the recommendations by DU Pont to thoroughly leak test must be followed.

    You may also have to adjust the TEVv and should use tables for R417a to check superheat & subcooling levels. Sometimes the cage / orifice size may need to be increased.

  10. #10
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Carrier Conversions

    After studying various reports I chose to convert with R417a. One unit has been sucessfully converted with excellant results but I'm waiting on Carrier to provide further gaskets etc (due in from the States soon I'm told) before I can proceed with the other 2.

    http://www.eurocooling.com/articlerhodia.htm

Similar Threads

  1. carrier fault codes
    By richelli in forum Trouble Shooting
    Replies: 5
    Last Post: 18-06-2010, 07:35 AM
  2. Carrier chiller oil migration
    By lowtech in forum Industrial
    Replies: 5
    Last Post: 30-04-2006, 04:11 PM
  3. carrier remote
    By superswill in forum Trouble Shooting
    Replies: 2
    Last Post: 26-04-2006, 09:17 PM
  4. Carrier spares
    By daddymac in forum Air Conditioning
    Replies: 6
    Last Post: 21-03-2006, 08:54 AM
  5. Required Control Wiring 50dp-020-910 Carrier
    By altaf22m in forum Air Conditioning
    Replies: 2
    Last Post: 08-08-2005, 06:08 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •