    Mar 2006
    newcastle upon tyne
    Exclamation fujitsu a/c running off generator
    Hi people been around for a short while but never posted so
    its my first time be gental please! i have been working on a
    semi perment trailer which has a small fujitsu a/c installed AOY25 all is well when im on site but intermittently it trips the breaker 25a d rated rcd, the supply comes from a 75a diesal genarater 225v checked cappy all ok start amps around 60a peak hold on amp clamp, wondered if genny has to much load but why would that trip my a/c breaker?
    11,025
    Re: fujitsu a/c running off generator
    Hi, welcome, yes the start load could trip things as the voltage will drop and the amperage will rise to compensate.
    Mar 2006
    newcastle upon tyne
    hi just an update, checked over today and the genny voltage is very unstable we are going to get a contractor to check the genny and report back i have also learned that the a/c has never tripped on a land power supply, worth knowing.
    cheers
    tait71
    Jul 2006
    57
    Is it tripping on RCD or MCB????
    Mar 2006
    newcastle upon tyne
    Thumbs up Re: fujitsu a/c running off generator
    its tripping an rcd d20 but the genny is loosing voltage on comp start, once the genny is sorted i will post and let you know whats happening then. cheers
  1. your opinons on fujitsu please
    By acgibo in forum Air Conditioning
    Last Post: 26-08-2009, 05:06 PM
  2. desperately seeking fujitsu
    By rbartlett in forum Air Conditioning
    Last Post: 04-08-2007, 09:06 PM
  3. Fujitsu
    By Abe in forum Air Conditioning
    Last Post: 21-07-2006, 08:36 AM
  4. Fujitsu AC not running
    By Team York in forum Air Conditioning
    Last Post: 05-07-2006, 07:52 PM
  5. fujitsu tech info
    By Krups in forum Air Conditioning
    Last Post: 01-12-2005, 07:41 PM