Hi people been around for a short while but never posted so
its my first time be gental please! i have been working on a
semi perment trailer which has a small fujitsu a/c installed AOY25 all is well when im on site but intermittently it trips the breaker 25a d rated rcd, the supply comes from a 75a diesal genarater 225v checked cappy all ok start amps around 60a peak hold on amp clamp, wondered if genny has to much load but why would that trip my a/c breaker?
-
10-07-2006, 11:41 PM #2
Re: fujitsu a/c running off generator
Hi, welcome, yes the start load could trip things as the voltage will drop and the amperage will rise to compensate.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
11-07-2006, 08:41 PM #3
Re: fujitsu a/c running off generator
hi just an update, checked over today and the genny voltage is very unstable we are going to get a contractor to check the genny and report back i have also learned that the a/c has never tripped on a land power supply, worth knowing.
cheers
tait71
-
15-07-2006, 12:03 AM #4
Re: fujitsu a/c running off generator
Is it tripping on RCD or MCB????
-
17-07-2006, 08:25 PM #5
Re: fujitsu a/c running off generator
its tripping an rcd d20 but the genny is loosing voltage on comp start, once the genny is sorted i will post and let you know whats happening then. cheers
Similar Threads
-
your opinons on fujitsu please
By acgibo in forum Air ConditioningReplies: 18Last Post: 26-08-2009, 05:06 PM -
desperately seeking fujitsu
By rbartlett in forum Air ConditioningReplies: 7Last Post: 04-08-2007, 09:06 PM -
Fujitsu
By Abe in forum Air ConditioningReplies: 9Last Post: 21-07-2006, 08:36 AM -
Fujitsu AC not running
By Team York in forum Air ConditioningReplies: 10Last Post: 05-07-2006, 07:52 PM -
fujitsu tech info
By Krups in forum Air ConditioningReplies: 11Last Post: 01-12-2005, 07:41 PM