Hi I have an area 14m long 8m wide 3m high which requires 23 c 50% rh on tight control
I am going to use chilled water and thyristor heaters
I have calculated at 20ACH that I need about 24kw cooling for the dehum based on 1.8 m3/s and off coil 12 degrees water 5 in 10 out with delta t of 5
What i am struggling with is the reheat to keep the tight control on the temp.
Need to calculate the size of heating required
this will be +/- 1 degree and 4% rh control
thanks