    I am facing a problem with ammonia chiller always trip in high temperature hot gas.
    our Mycom i160LL when it run 100 percentage load it will trip.50 percentage load it will run.so please suggest me what need to check.



  2. #2
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    508
    Rep Power
    17

    Re: hot gas high temperature

    Calibration of hot gas temperature sensor
    Motor current
    Oil supply temp
    Oil supply pressure/flow
    Suction superheat
    Discharge pressure
    Operation of liquid injection

  3. #3
    Join Date
    Aug 2022
    Location
    United States
    Posts
    29
    Rep Power
    0

    Re: hot gas high temperature

    Those are all excellent suggestions. I would add, there should also be a hand metering valve that feeds oil to the rotors. This oil essentially acts as a "seal" between the rotors and the casing. If there is not enough injection oil, you will have "blow by" and elevated discharge temperatures. Too much injection oil will reduce performance and use up hp. You might try opening this valve a bit more and seeing if oil temperatures drop noticeably when you do so.

    Good luck,
    MrFreez717

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,375
    Rep Power
    39

    Re: hot gas high temperature


  5. #5
    Join Date
    Jan 2023
    Location
    Austria
    Posts
    11
    Rep Power
    0

    Re: hot gas high temperature

    Hi,
    maby the suction pressure drops by 100% and the compressor is out of range?

  6. #6
    Join Date
    Jun 2009
    Location
    saudia arabian
    Age
    53
    Posts
    29
    Rep Power
    0

    Re: hot gas high temperature

    i open suction filter of this compressor it is cleaned and fixed it back same issue..

  7. #7
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: hot gas high temperature

    Believe most of these as packaged have economizer as brazed plate heat exchanger. If there is a regulator and solenoid between that and the compressor side port, I would check their operation especially if there is additional compressors on this same suction. If the side port takes on too much vapor as heat load in subcooling liquid, the machine will tend to overheat. Easy to check for most circuits: Close the vapor line to the sideport and see if the machine will run at 100% load.