hot gas high temperature
Dear All,
I am facing a problem with ammonia chiller always trip in high temperature hot gas.
our Mycom i160LL when it run 100 percentage load it will trip.50 percentage load it will run.so please suggest me what need to check.
-
19-09-2023, 08:24 PM #2
Re: hot gas high temperature
Calibration of hot gas temperature sensor
Motor current
Oil supply temp
Oil supply pressure/flow
Suction superheat
Discharge pressure
Operation of liquid injection
-
19-09-2023, 09:29 PM #3
Re: hot gas high temperature
Those are all excellent suggestions. I would add, there should also be a hand metering valve that feeds oil to the rotors. This oil essentially acts as a "seal" between the rotors and the casing. If there is not enough injection oil, you will have "blow by" and elevated discharge temperatures. Too much injection oil will reduce performance and use up hp. You might try opening this valve a bit more and seeing if oil temperatures drop noticeably when you do so.
Good luck,
MrFreez717
-
20-09-2023, 08:59 AM #4
Re: hot gas high temperature
This might help!
https://mayekawa.ru/netcat_files/160/218/i_series.pdf
-
22-09-2023, 07:44 PM #5
Re: hot gas high temperature
Hi,
maby the suction pressure drops by 100% and the compressor is out of range?