    Hi

    what can be cause of discoloration oil in Reciprocating Compressor?
    awaiting your kind input.
    Thanks



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Reciprocating Compressor

    Contaminants or high heat. Running the system with continued high head pressure.

  3. #3
    Join Date
    Jul 2007
    Location
    Czech
    Age
    61
    Posts
    374
    Rep Power
    18

    Re: Reciprocating Compressor

    Water as far as ammonia plants are concerned.

    Josef.

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Reciprocating Compressor

    Air in system, oxidation.
    Oil separator oil returning contaminated oil from coating on pipes.
    Oil type from the past could be poor quality.
    Last edited by RANGER1; 13-05-2023 at 10:53 PM.

  5. #5
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14

    Re: Reciprocating Compressor

    i joined newly this plant. plant type Ammonia V1400 Grasoo earlier they were using Petro Canda oil. after on cost saving they shift to Mobil Arctic 300. since long time did not major overhauling or maintenance of compressors.

  6. #6
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: Reciprocating Compressor

    Hi Shaaf,
    Petro canada oil( Reflo 68??) is from hydrotreated familly witch are strongly recommended by Grasso.
    Artic oil 300 is basic mineral oil subject to cokefaction at high temperature. also accepted by Grasso.
    your V1400 is probably without oil cooler, and if you are operating close to its limits; discharge temp can be very high.
    This is if the oil tend to be brown,
    if it's grey it's an other story...

  7. #7
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14

    Re: Reciprocating Compressor

    oil is like coke

  8. #8
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: Reciprocating Compressor

    So what are the operating conditions so that I could check them?
    Is it a package or an industrial plant? how many running hours?
    suction and discharge pressure?
    suction superheat?
    operated with VSD? if yes, max and min speed?
    minimum capacity step used ?
    oil separator or not? any oil analysis?

    is there a GMM (Grasso Maintenance Monitor) at the left side of the oil pump?
    if yes do you have access to check the operating conditions.

    Artic oil 300 is much more sensible to high discharge temperature and water contamination in refrigerant

    The switch to Artic 300 is a bad choice for stability