    Full power down comms ?



    Daikin RXS50K2V1B
    Hi I'm reading 240v on the comms (3) ???
    I just replaced both the outdoor PCB. Was told to do this but didn't originally diagnose the fault. Tried to run, straight away the system has gone back in fault. U4. And took out the PCBs again. Indoor did start for a few seconds but then thats when it faulted. Still waiting for daikin to ring me back, but just wondering if anyone has an idea of what's going on. Thanks



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Full power down comms ?

    What are your wiring connections

  3. #3
    Join Date
    Feb 2009
    Location
    England
    Posts
    6
    Rep Power
    0

    Re: Full power down comms ?

    Wiring connections?
    1 - live, 2 - neutral, 3 - comms, - earth
    Is this what you need?
    Note - I can take 3 - comms out the condenser and test it. It's
    still 240v when should fluctuate to around 40v I think

  4. #4
    Join Date
    Feb 2009
    Location
    England
    Posts
    6
    Rep Power
    0

    Re: Full power down comms ?

    Daikin never rang me back, I'll have to try again tomorrow

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Full power down comms ?

    Are you measuring terminal 3 to neutral or live ?
    Measuring ac or dc

  6. #6
    Join Date
    Feb 2009
    Location
    England
    Posts
    6
    Rep Power
    0

    Re: Full power down comms ?

    3 to earth. 247v last I checked

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Full power down comms ?

    Comms should be measured between 3 and neutral in dc

    Check the fan motor for earth fault
    https://www.manualslib.com/manual/96...page=78#manual

  8. #8
    Join Date
    Feb 2009
    Location
    England
    Posts
    6
    Rep Power
    0

    Re: Full power down comms ?

    Yeah your right. Outdoor fan motor has gone. And I feel a like fool haha ��