    Daikin L4 fault



    Hi we have a RMX140JVMC system that’s going out on L4 fault .Daikin have told us to change 2 boards which we have done and the fault is still there .Any suggestions to get the system to run ?



  2. #2
    Join Date
    Feb 2017
    Location
    UK
    Posts
    112
    Rep Power
    9

    Re: Daikin L4 fault

    Quote Originally Posted by snow_man View Post
    Hi we have a RMX140JVMC system that’s going out on L4 fault .Daikin have told us to change 2 boards which we have done and the fault is still there .Any suggestions to get the system to run ?
    on the 2 pcb's you replaced did they come with the thermal paste already on them? if not did you add the thermal paste.
    Also did the boards come with a new fin thermistor? if not did you replace the thermistor?

  3. #3
    Join Date
    May 2010
    Location
    japan
    Posts
    19
    Rep Power
    0

    Re: Daikin L4 fault

    ttp://acforest.starfree.jp/daikin-sky/ec/L4.htm
    This site is in Japanese.
    I wish I could serve you

  4. #4
    Join Date
    Sep 2023
    Location
    Los Angeles
    Posts
    1
    Rep Power
    0

    Re: Daikin L4 fault

    Quote Originally Posted by snow_man View Post
    Hi we have a RMX140JVMC system that’s going out on L4 fault .Daikin have told us to change 2 boards which we have done and the fault is still there .Any suggestions to get the system to run ? geometry dash meltdown
    It may be due to an error in increasing the temperature of the inverter's radiation blades. Fin temperature increases due to short circuit.