    Icing Evaporator



    Hi,

    We have a cold room approx 3mx3mx4.5m high running @ a set temp of 1-4 degrees Centigrade. The Evap unit is a twin fan Muller MLV100, running on R404a gas. The compressor is a copeland running 1 other room and a a freezer. The Room cycles in/out throught the control of a bulb thermostat, opening and closing a solenoid in the supply line.

    The problem we are having is the evaporator coil continuously icing, which will cause flood back to the compressor, icing it up as well. I then have to isolate the solenoid for around 6 hours to allow the unit to defrost then switch it back on again. I have cleaned the evap coil, checked both fans for air flow, which seems low but not bad. the tx valve bulb is in place. Drier was replace about 6 months ago (the drier runs all 3 rooms). The evap may take a week to ice or it might take 4 hours after a manual defrost.

    The evap coil is old and was desighned for the older gasses, not the R404a. There is no defrost fitted but the room has run fine like this for years. The door seals are in sound condition and no other room leaks can be sighted but being an old room there may well be.

    My question is, Would a new evap coil fix the problem ($1500 fitted), or are there some other steps that can be taken to solve the problem eg. new tx valve?
    Last edited by brad72; 19-01-2007 at 06:04 AM.



  2. #2
    LRAC's Avatar
    LRAC is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Sep 2006
    Location
    Midlands
    Posts
    453
    Rep Power
    18

    Re: Icing Evaporator

    Hi brad72

    before going any further you really do need to check the superheat settings, this may reveal a TXV fault but you wont know without doing more tests.

    Kind regards
    Lrac

  3. #3
    Join Date
    Jun 2002
    Location
    Mumbai, India
    Age
    66
    Posts
    25
    Rep Power
    0

    Re: Icing Evaporator

    Hi brad72
    With a set room temperature of 1 to 4 Deg. C, the compressor evaporating temperature would be -4.5 Deg.C just before cut-off, if the coil was selected for 10 Deg. F T.D. This is likely to cause frosting. However if there was no frosting problem earlier, it could mean that the evap. was sized for lower than 10 Deg. F TD - which would mean a bigger evap.
    This seems to be a case of system imbalance. Either the compressor has a larger capacity or the coil efficiency has reduced due to ageing and change of refrigerant.
    In case you are having an open type belt driven compressor you could try reducing the compressor speed to reduce the compressor pumping which will improve the suction pressure and hence temperature.
    The compressor suction temp. should be no lower than that equivalent to 26 Deg. F evaporating temp. I.e. about 64 PSIG.
    All the best
    S.M.Gokhale

  4. #4
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Icing Evaporator

    hi matey, how about mounting a small simple time clock on the back wall on the electrics side of the cooler inside a plastic adatable box,run a couple of cables into the cooler or wherever the solinoid is fed from and switch the solinoid with the defrost clock,try 4 x 30 mins for a start, its worth a try,should be o/k,

    as theese systems get older they do get new problems,bit like me realy, go for that before making a meal of it, cheers.

  5. #5
    Join Date
    Jan 2007
    Location
    Poland
    Age
    49
    Posts
    12
    Rep Power
    0

    Re: Icing Evaporator

    If following are met:
    -superheating about 2....5 K => at evaporating temp. ~-7oC .... -4oC at steady run for
    stabilized room temperature
    -at such temperature case only 2 or 3 electric defrost cycles/24 h are resonable, defreost ended by evoprator temperature, defrost sensor placed as far as possible from defrost heater in air's flow direction
    -TEV mounted properly, nozzle is selected for evaporator capacity, TEV bulb mounted at rising suction pipe just after evaporator discharge outlet
    -each section of evaporator is equally fed with refrigerant
    -capacity of compressor and evaporator are more or less equal
    no icing should appear.

    If not a hughe quantity of moister is driven into coldroom.

    Brgpavel

  6. #6
    Join Date
    Jan 2007
    Location
    Australia
    Age
    51
    Posts
    5
    Rep Power
    0

    Re: Icing Evaporator

    Hi Guys,

    Thanks for the responses. Will give them a try.

    - We have thought of a defrost timer but because the cold room is used to hold pallets of egg pulp, we are a little concerned of excess temperature rise. I also assume that i would have to switch the fans off at the same time to stop water bing sprayed around the room?

    -I will have to find a fridgy willing to check the superheat etc. Most just want to install a new evap.

    -But, if we install a new evap unit and the problem is excess humidity in the room, will this new unit also suffer from the same problem. Is it worth me caulking all the exterior joins on the room?

    Thanks
    Brad

  7. #7
    Join Date
    Jun 2005
    Location
    Stoke on Trent
    Age
    62
    Posts
    588
    Rep Power
    19

    Re: Icing Evaporator

    Has it always been used for egg pulp storage, not used or designed originally for a different product, have repairs been carried out in the last few months, as it always been troublesome or only recently, so my understanding is that there are 2 high temp cold rooms and 1 freezer coldroom run off 1 copeland comprerssor, is the other high temp cold room running ok? Now finally, has the evaporator been pressure washed to clean and is the thermostat accurate, I am a big fan of replacing old stats and timers etc with an elliwell, at least you can see exactly what it is doing from outside ofthe room. Have you thought about fitting a temporary chart recorder in the room to confirm temperatures and when ice ups actually start. Is there any capacity control on the compressor.
    Last edited by Andy W; 20-01-2007 at 07:20 AM.

  8. #8
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Icing Evaporator

    i still go by what i say, ALL cold rooms with a standard spec should have a defrost system,no you DONT stop the fans, just shut the solinoid down and run the fans continiously,theres a thought,they dont stop on the thermostat do they ? if they do alter that before doing anything else and try it, you wont blow water out,it should just drain away as normal unless the evap is blocked or theres a problem, try 20 min defrosts to start then,if your product is down to temp the defrost cycle will only raise the air temp a bit and not enough to bother the product . cheers.

  9. #9
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Talking Re: Icing Evaporator

    Install electrical heater for defrost and some Caerel for defrost regulation (controls fan,el.heater,time of defrost and goes in defrost by temperature on coil).

    Total cost for example:
    Heaters 100$ Australian
    Carel 150$ Australian

    Best regards,
    Renato

  10. #10
    Join Date
    Jan 2007
    Location
    Australia
    Age
    51
    Posts
    5
    Rep Power
    0

    Re: Icing Evaporator

    hi
    Thanks again for more advice. A cheap defrost timer would certainly help the problem.


    In reply to Andy, the room has been used for this purpose for 3 years now. I pressure cleaned the evap unit for the 1st time a couple of days ago. Had noticed alot of muck on the coil. All the fins are intact and straight. The other cold room goes fine, and never ices, even if the door is left open for 5 minutes. The frrezer @ -26 centigrade is also fine. The thermostat was replaced 2 months ago and the entire sysyem was regased 1 month ago as there was a big leak in 1 of the old driers, which was redundent and no has now been removed.

    The fans however don't seem to put much air through the coil. Also, the fans are mounted at an angle, about 60 degrees. I assume poor air flow through the coil can also cause problems.

    Thanks

  11. #11
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Icing Evaporator

    Quote Originally Posted by old gas bottle View Post
    hi matey, how about mounting a small simple time clock on the back wall on the electrics side of the cooler inside a plastic adatable box,run a couple of cables into the cooler or wherever the solinoid is fed from and switch the solinoid with the defrost clock,try 4 x 30 mins for a start, its worth a try,should be o/k,
    What O.G.B. is saying would fix the job.

    Defrosting a coil for 30 mins with the fans running will not cause any temperture concerns at all.
    So long as you are keeping the temperture above 1 deg c then there is no need for heater assisted defrost.

    It would take about 10 minutes to fit a timer and put an end to your troubles.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  12. #12
    Join Date
    Jan 2007
    Location
    Australia
    Age
    51
    Posts
    5
    Rep Power
    0

    Re: Icing Evaporator

    Well gentlemen , i think i have fixed the problem.

    Fired the room up today after pressure cleaning the coil and the air flow is alot better. Also, after reading a another thread about snow in a blast freezer, i sat in the room for 15 minutes in the dark, waited for my eyes to adjust, and found....a 4 meter x 1/4 inch gap down 1 wall. sometime in the last week our forklift drivers must have hit the wall with pallets and pushed it out. Sealed it now. It would also appear that when the room was built, they skimped on mastic as the join that split had none!

    A long story short, room is cycling great and practically no ice on the coil. I will still however fit a defrost timer to the unit as the room has planty of traffic throughout the day.

    Thanks again for all your help. Better do the same test for the other room and freezer...-26 centigrade....bbbrrrrrrr

  13. #13
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    242
    Rep Power
    21

    Re: Icing Evaporator

    hey brad72,

    good to see you sorted the fault with the gap

    good idea to add timeclock to your control circuit should be able to pick one up for around $30 cant go wrong
    "Old fridgies never die, they just run out of gas!"

  14. #14
    Join Date
    Mar 2007
    Location
    INDIA
    Age
    42
    Posts
    31
    Rep Power
    0

    Re: Icing Evaporator

    Hi Matey
    Why don't you try out the hot gas bypassing method to avoid the liquid slugging to the compressor.This will help you to maintain the superheat also.

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Icing Evaporator

    Increase the differential on the new thermostat.

  16. #16
    Join Date
    Sep 2006
    Location
    Bristol
    Age
    35
    Posts
    20
    Rep Power
    0

    Re: Icing Evaporator

    Glad its sorted - but make sure you fit a timeclock, I have never come across a cold room that has no defrosts, silly if you ask me.
    I would have the fans switch off on defrost - so if when on defrost and the door is opened it does not draw any warm air in.
    Last edited by Takeshi; 01-03-2007 at 06:43 PM.

  17. #17
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Icing Evaporator

    Quote Originally Posted by Takeshi View Post
    I would have the fans switch off on defrost - so if when on defrost and the door is opened it does not draw any warm air in.
    The air blowing through the coil is what defrosts it.

  18. #18
    Join Date
    Jun 2007
    Location
    darwin
    Age
    46
    Posts
    13
    Rep Power
    0

    Re: Icing Evaporator

    What about installing a evap pressure regulator to the cool rooms this will stop the icing up.

  19. #19
    Join Date
    Aug 2009
    Location
    USA
    Age
    62
    Posts
    44
    Rep Power
    0

    Re: Icing Evaporator

    I would go with the easiest route first and do what Gary says = increase the differential time.

    Increasing the time to when the system cuts back in will give the fan a longer time to defrost the evap coil.

  20. #20
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Icing Evaporator

    If this system is still icing up after 3 years then the original poster should be sacked...
    19-01-2007, 04:25 AM
    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  21. #21
    markie_022's Avatar
    markie_022 Guest

    Re: Icing Evaporator

    hi guys,,

    i just want to know what is the cause of icing forming in accumalator? what are things to do? thanks.....