    Midea Headaches



    Afternoon all,

    Has anyone got any ideas on this issue, I was called to a multisplit midea unit the other day with reports of the units not working in heat and constantly in defrost.

    The office was at 18 in the morning and they set the unit to 23, when I arrived (late afternoon) the room was only at 19.

    No faults and no errors on indoor or outdoor, run unit in forced cooling and the pressures were
    L-7bar and H-10bar cooling fine, when switching to heating both pressures at 30bar, my initial thought was 4 port valve not sliding over properly, I tested the temps on the valve and going by the temps recorded the valve seems to of fully changed over.
    Tested the 4 port valve with a magnet and it seems to work but I'm concerned with the equal high pressures when on heat.

    Technical were stumped too.



  2. #2
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    452
    Rep Power
    17

    Re: Midea Headaches

    What refrigerant?
    Where are you taking the pressure readings from?
    What type of expansion device(s) does it have? For cooling mode and for heating mode. Sorry never looked at Midea stuff before.

    Its not just a restriction on the expansion device (strainer/check valve if there) used for the heating mode? That could give you HP at the access valves on the shut off valves where you pipe up the outdoor unit. And give too low a temp at the condenser, assuming its defrosting based on a thermistor reading.
    Last edited by seanf; 30-03-2023 at 07:57 PM.
    Interested to hear about opportunities to learn - linkedin.com/in/s34nf

  3. #3
    Join Date
    Feb 2017
    Location
    UK
    Posts
    112
    Rep Power
    9

    Re: Midea Headaches

    Quote Originally Posted by seanf View Post
    What refrigerant?
    Where are you taking the pressure readings from?
    What type of expansion device(s) does it have? For cooling mode and for heating mode. Sorry never looked at Midea stuff before.

    Its not just a restriction on the expansion device (strainer/check valve if there) used for the heating mode? That could give you HP at the access valves on the shut off valves where you pipe up the outdoor unit. And give too low a temp at the condenser, assuming its defrosting based on a thermistor reading.
    Sorry, I was in a rush yesterday posting this.

    Gas is 410a.
    Unfortunately the only place I can gauge up is the shut off valves where the pipe is connected.
    It has an EEV inside the condenser for cooling, heating not too sure, I'm not too familiar with the unit either.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Midea Headaches

    Coolin and 7 bar LP and 10 bar HP and that's OK ? No, this isn't ..
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Feb 2017
    Location
    UK
    Posts
    112
    Rep Power
    9

    Re: Midea Headaches

    Quote Originally Posted by Peter_1 View Post
    Coolin and 7 bar LP and 10 bar HP and that's OK ? No, this isn't ..
    Never said it was okay. I said it was cooling fine, it's the 30bar equal pressures that concerned me more

  6. #6
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    452
    Rep Power
    17

    Re: Midea Headaches

    Quote Originally Posted by TrickyRikki View Post
    Sorry, I was in a rush yesterday posting this.

    Gas is 410a.
    Unfortunately the only place I can gauge up is the shut off valves where the pipe is connected.
    It has an EEV inside the condenser for cooling, heating not too sure, I'm not too familiar with the unit either.
    Maybe theres more than one restriction.
    Do Midea units give you a pressure transducer reading you could use for the suction?
    I guess just look for the point where its frosting up. See if Technical can send you a P&ID.
    Interested to hear about opportunities to learn - linkedin.com/in/s34nf

  7. #7
    Join Date
    Feb 2017
    Location
    UK
    Posts
    112
    Rep Power
    9

    Re: Midea Headaches

    Quote Originally Posted by seanf View Post
    Maybe theres more than one restriction.
    Do Midea units give you a pressure transducer reading you could use for the suction?
    I guess just look for the point where its frosting up. See if Technical can send you a P&ID.
    There is a small led tube display (the 2 8's that light up) after looking in the technical manual it does state you can read the values but when I tried to swap what it was showing me it wouldn't, I spoke with technical and they was meant to be getting back to me on how to do it but as of yet no response.

    I will be back in that area next week so will go look for frosting ect

  8. #8
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Midea Headaches

    10 bar head pressure is very low for 410a have you checked the gas charge

Tags for this Thread