hot gas defrost line sizing
Hello Folks
Is there any guidelines or methods to size the defrost line for a multi evaporator multiplex system for evaporator (walk in rooms)
what is the recommended velocity range and pressure drop (temperature rise)?
TIA
-
04-03-2023, 07:40 PM #2
Re: hot gas defrost line sizing
Velocity range as with all gasses... 8 to 12 m/s and 1 to max 2K equivalent pressure drop
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
25-03-2023, 09:42 AM #3
Re: hot gas defrost line sizing
Hi Everyone
Hot gas defrost is a common method of removing ice buildup on the evaporator coil in a refrigeration system. The sizing of the hot gas defrost line depends on several factors, including the size of the evaporator coil, the amount of ice buildup, the refrigerant being used, and the length of the defrost line..
-