    Unhappy Technical difficulties



    Hi all,
    I have been working on a Carrier Primeline reefer for the past two weeks, however, I am unable to solve the problem.
    Reefer model #69NT40-561-018
    The system has a restriction, and the compressor runs in a vacuum after the three-bump start.
    Controller alarm: AA28 - low suction pressure
    replace filter drier, replaced all transducers: EPT, SPT &DPT
    Replace EEV complete body and coil, replace DUV complete body and coil, replace evaporator temp sensor ETS1 and EST2
    The controller interchange (on problem with the controller)

    Thanks in advance,
    KRampersad



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Technical difficulties

    Controller closes the EEV because you already replaced all other possible causes (but why if you were not certain about the real cause/problem?)?
    Seems very basic schematic...
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    451
    Rep Power
    17

    Re: Technical difficulties

    What does it do on the Pre-trip test?

    Did you blow through the pipework with nitrogen to check for any restrictions while you had components removed?