    Coolpack error



    Hello colleagues,

    Draw a cycle in Coolpack
    R134a, TC 40°C; 5K SH and 5 K SC, TE= -5°C.
    In Cycle analysis, enthalpy at end of evaporator = 257 kJ/kg
    Same cycle drawn in Refrigeration Utilities of Coolpack and enthalpy is there at the same point around 400 kJ/kg (zoomed in)
    Where's this difference coming from?


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    452
    Rep Power
    17

    Re: Coolpack error

    Does it give the same changes in Enthalpy?
    Maybe different people wrote those parts of coolpack?
    Interested to hear about opportunities to learn - linkedin.com/in/s34nf

  3. #3
    Join Date
    Aug 2022
    Location
    United States
    Posts
    28
    Rep Power
    0

    Re: Coolpack error

    Agree with seanf, check to see if the enthalpy CHANGES are the same. The "zero point" for enthaply seems to be an arbitrary decision, so the values at a given point may differ, but the change between two states should yield the same result. I'm old so use tables mostly, but my favorite defines enthalpy at 0 for -40F (or -40C) saturated liquid.

    MrFreeze

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Coolpack error

    Hello, change in enthalpy is indeed the same for both codes but anyhow, a given refrigerant has at a certain point in a log ph always a fix enthalpy which should be always the same.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  5. #5
    Join Date
    Aug 2022
    Location
    United States
    Posts
    28
    Rep Power
    0

    Re: Coolpack error

    Same topic discussed in earlier thread here: https://www.refrigeration-engineer.c...ative-enthalpy

    As stated, -40C is "typical" place to assign 0 enthalpy for saturated liquid, but you could use a different temperature for this, as some sources do. Since the change in enthalpy is the point of interest, it does not matter where you assign a zero value - the difference between state points is what defines the work done.

    In my most used source, all refrigerants (ammonia, CO2, R507, etc) have 0 enthalpy for -40F saturated liquid. This is not a crazy coincidence, but rather a conscious choice to use a common reference point. Obviously all these different substances to not have the exact same internal energy as each other.

    MrFreez717