    Question Ammonia Receiver temperature is increasing



    We have recently commissioned our new refrigeration plant. It is working fine the only problem is when we open the Equalizer line valve connecting the evaporative condenser and receivers, the receiver temperature increases.
    We have 2 nos of receivers and 3 nos of evaporative condensers.



  2. #2
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Ammonia Receiver temperature is increasing

    Have you considered that this may be exactly what should happen?
    With the Equalizer line closed the Condenser may be filling with Refrigerant and Sub Cooling the liquid.

  3. #3
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    451
    Rep Power
    17

    Re: Ammonia Receiver temperature is increasing

    Increasing to what temperature?
    And at what discharge/condenser/receiver pressure?
    Is it all of the receiver that warms up, or just the top where the vapour is?
    Are the two receivers warming up to the same temperature, or just one?