    Expansion valve making pulse vibration



    I have a 9 kw liquid/water heat pump. Refrigerant is R410A. Because of a broken pipe i changed the condensor plate heat exhanger. After the change, the expansion valve has started to make pulse vibration/noise 5-10 minutes after startup. When the vibration occurs, i can se some bubbles in the sight glas.

    The water pump for the evaporater have 3 speeds. There is less vibration at the lowest speed, and if i run the pump on full speed, the vibration is constant, not only pulses.

    I tried to increase the superheat, but it did not solve the problem.
    What can the reason for this be? Can it be to much refrigerant?



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Expansion valve making pulse vibration

    HenKri,
    Does the pulsations mimic discharge pressure.
    Have seen it happen with a different setup than heatpump where PHE condenser water control valve was modulating.
    If system overcharged, would it be seen by high than normal discharge pressures.

  3. #3
    Join Date
    Jun 2006
    Location
    jiansu
    Posts
    38
    Rep Power
    0

    Re: Expansion valve making pulse vibration

    which brand of the expension valve you used? danfoss valves maybe have this problem I have met once.