    Hitachi RCI-2,0-FSG2 - Ventilation speed variation



    We are facing a problem at one Hitachi RCI unit, part of a Set Free system.
    The first problem was the freezing sensor, which we have already replaced by a new one.
    Now, the ventilator is oscilating its speed. That speed up and slowdown without any user command.
    The air comming from the RCI is at the correct set temperature. So, I assume the refrigerating gas is circulating in the unit.
    The problem is the speed of the ventilator indeed, that doesn`t keep running continously.
    Does someone know the possible reason of this problem ?

    Thank you in advance.
    Regards,
    Rafael



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Hitachi RCI-2,0-FSG2 - Ventilation speed variation

    Check the refrigerant charge, i think fan speed is dictated by coil temperature. Also check the evaporator fan motor is not over heating and tripping itself out.