    Im having issues with a City multi PURY P250 YMF.
    It seems to run in heating mode fine - but when it runs in cooling it trips out on HP straight away. I suspect that the 4 way valve may be stuck? how can I prove this - and if it needs to be changed - how big a job is that?
    thanks
    Aug 2007
    Russia
    139
    22
    Re: city multi PURY P250 YMF
    I would think of the check valve CV1.
    Sep 2022
    uk
    13
    Thanks, I intend having a look at this in the next few weeks- before we need To go in to cooling mode. Apparently Mitsubishi do a check valve repair kit - you ever overhauled one ? I have units either side so only have access from the front and rear
    Aug 2007
    Russia
    139
    22
    I don't think any check valve is reparable, it supposed to be changed.
    BTW, besides CV1, the CV7 check valve could be a problem. This valve works in cooling mode only.