    Zanotti 20s high pressure



    hi I have a zanotti 20s type of gas r404 and from the label I read 1.10 KG I change the deindrator filter I replace the orifice I do a vacuum and load the system at start-up I realize that in high pressure it works at 25 bar and in low pressure 7 bar kvl pressure 2,8 bar it is 20 minutes active after high pressure goes into error the liquid indicator is not full but in the middle what can it depend on? condenser all in all clean thank you in advance i'm using translator i don't speak english very well i hope i was clear
    Last edited by Androidkil; 14-09-2022 at 10:59 AM.



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Zanotti 20s high pressure

    .

    Hello.

    Your English is better than my Italian .

    Assuming you did not contaminate the system when you broke the vacuum?

    Is the condenser fan spinning at the correct speed?

    Do a standing test.
    Stop the machine with your gauges attached and let it totally equalise in pressure with the
    ambient temperature. If the pressure shown on the gauges is higher than the saturation temperature
    of the refrigerant at the ambient temperature it is stood in, there is air inside the system.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Jun 2022
    Location
    Italia
    Posts
    2
    Rep Power
    0

    Re: Zanotti 20s high pressure

    temperature 28 degrees

    HP 9.85
    LP 9.76

  4. #4
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Zanotti 20s high pressure

    .

    R404A at 28degC is about 12bar.

    Did you put pure R404A in?
    404A does lose some of its blend if it has a leak.
    R404A is made of 3 refrigerants and the R134a part always leaks first which de-stabilises the pressure.

    Is it possible the gas you put in was used and came from a system that had a leak?

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  5. #5
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: Zanotti 20s high pressure

    Is condenser fan spinning and in correct rotation also are you checking pressures with condenser lid partly off you can only check sight glass when condenser fan is full chat please check your getting a full 12 volts to fan

  6. #6
    Join Date
    Nov 2022
    Location
    Nepal
    Posts
    5
    Rep Power
    0

    Re: Zanotti 20s high pressure

    Quote Originally Posted by Rob White View Post
    .

    Hello.

    Your English is better than my Italian .

    Assuming you did not contaminate the system when you https://cbdshop.club/ the vacuum?

    Is the condenser fan spinning at the correct speed?

    Do a standing test.
    Stop the machine with your gauges attached and let it totally equalise in pressure with the
    ambient temperature. If the pressure shown on the gauges is higher than the saturation temperature
    of the refrigerant at the ambient temperature it is stood in, there is air inside the system.

    Rob https://telegrambetting.club/

    .
    Hi Rob,

    Thanks for the warm welcome to the forum! I appreciate the advice and I'll make sure to take it onboard. I'm sure I'll have plenty more questions in the future, and I'm grateful to have such a knowledgeable community here to answer them.