    Jan 2022
    Algeria
    Air filters Max pressure advised
    Greetings,
    I've got a question, so I have this air handling unit that contains 2 filters (Galvanized frame G4 and Bag filter F7) attached together.
    At what pressure differential should I set up the manometer, for the alarm of the filter contamination?
    F7 Pressure Max pressure advised is 200 Pa
    And the G4 is 140 Pa
    Do I add the two values together? 340 Pa?
    Available for more information.
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    May 2006
    Yorkshire
    72
    417
    Re: Air filters Max pressure advised
    I wouldn't recommend using one manometer across both bag and panel filters. Others however may have a different opinion.
    Ideally, as the panel and bag filters have different characteristics and pressure drops you need to use two manometers, one for each type of filter.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
    11,025
    Agreed ^^^^^
    Use one manometer per filter type/bank.
    The panel filter collects most of dirt so could be changed several times before the bag needs replacing.
    Dec 2022
    8
    I totally agree with you, nice advice.
