    Grasso Tripping breaker



    I went through problem with one of Grasso compressor its W series with 450Kw motor
    problem is it is causing the breaker to trip when it shifts itself from star to delta.
    Following things checked.
    Motor insulation is okay
    Cable insulation is okay
    Star timing extended and motor working fine
    All things contactors, breakers checked,swapped everything fine.
    When motor decoupled it was working fine (Shifting properly from star to delta)
    Slide calibrations done found normal.
    Can anybody help me on it



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Grasso Tripping breaker

    maltaf,
    Some other possibilities could be mechanical.

    To much oil in compressor (overfilled, suction check valve failed.
    To much oil in compressor oil separator
    GEA usually recommend minimum 10 minutes between starts due to oil pump filling up machine.
    Compressor not fully unloaded, check above, recalibrate again.

    If above okay & not already the case, lower compressor package, oil separator etc to suction pressure to help for easier starting, less start up load.
    Sometimes a line exists to do this when compressor off, a line small between discharge & suction cracked open.
    Last edited by RANGER1; 25-08-2022 at 10:21 AM.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Grasso Tripping breaker

    Also check that the breaker is not failing.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Grasso Tripping breaker

    Hi it might be worth if you have not already done so. In checking the timer unit that switches over the Star, Delta contacts. If the switch over is not clean then the resultant Load especially from the star contact, can take the breaker out.
    Just a thought. as i have seen this before.
    Cheers Grizzly
    Despite the High Cost of Living it still remains Popular!

  5. #5
    Join Date
    Aug 2022
    Location
    Pakistan
    Posts
    6
    Rep Power
    0

    Re: Grasso Tripping breaker

    Thanks for your reply

    THERE IS NO OVERFILLING OF OIL.
    OIL IN THE SEPARATOR IS 1/3 OF GLASS
    ADJUSTED DELAY WAS ALREADY 10 MINUTES
    TRIED CALIBRATIONS AND RECHECKED AND FOUND NORMAL
    ONLY THING LEFT IS THE CHECK VALVE

  6. #6
    Join Date
    Aug 2022
    Location
    Pakistan
    Posts
    6
    Rep Power
    0

    Re: Grasso Tripping breaker

    breaker replaced with other one , it is okay

  7. #7
    Join Date
    Aug 2022
    Location
    Pakistan
    Posts
    6
    Rep Power
    0

    Re: Grasso Tripping breaker

    but it is working fine when motor decoupled.

  8. #8
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Grasso Tripping breaker

    maltaf,
    Has this machine been running in the past & now has a problem?
    Or is it new compressor package.

    What is suction & discharge pressures in system & package itself at start up.

  9. #9
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Grasso Tripping breaker

    Hi All of the above by Ranger are relevant!
    Just a thought have you put a Clamp meter on the incoming supply to see what the Comp is pulling Amperage wise?
    Star Delta timers are normally around 7 seconds duration. Just as a question which Breaker is Tripping?
    What is your oil temp by the way on start-up?
    Good luck Grizzly
    Despite the High Cost of Living it still remains Popular!

  10. #10
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Grasso Tripping breaker

    Maximum oil pressure 350 kpa above discharge pressure at all times, otherwise damage may occur mechanically.
    If compressor not connected, of course no problem, as no load on start up.
    Calibration of slide valve always best when compressor running.
    So could still be an issue.

  11. #11
    Join Date
    Aug 2022
    Location
    Pakistan
    Posts
    6
    Rep Power
    0

    Re: Grasso Tripping breaker

    Quote Originally Posted by RANGER1 View Post
    maltaf,
    Has this machine been running in the past & now has a problem?
    Or is it new compressor package.
    it was running earlier.

    What is suction & discharge pressures in system & package itself at start up.
    suction pressure 2.25 bar discharge 12.0 bar

  12. #12
    Join Date
    Aug 2022
    Location
    Pakistan
    Posts
    6
    Rep Power
    0

    Re: Grasso Tripping breaker

    Quote Originally Posted by Grizzly View Post
    Hi All of the above by Ranger are relevant!
    Just a thought have you put a Clamp meter on the incoming supply to see what the Comp is pulling Amperage wise?
    Star Delta timers are normally around 7 seconds duration. Just as a question which Breaker is Tripping?

    What is your oil temp by the way on start-up?

    Good luck Grizzly
    main breaker. If we extend the timing breaker from substation goes trip.
    oil temp 36C

  13. #13
    Join Date
    Sep 2005
    Location
    UK
    Age
    42
    Posts
    196
    Rep Power
    20

    Re: Grasso Tripping breaker

    check the amp draw while it's starting up in star before it switches to delta?

  14. #14
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,758
    Rep Power
    46

    Re: Grasso Tripping breaker

    Just a thought have you put a Clamp meter on the incoming supply to see what the Comp is pulling Amperage wise?
    Great minds think alike?
    That's exactly what i was trying to imply. You can get a huge inrush between switching contacts.
    main breaker. If we extend the timing breaker from substation goes trip.
    Not sure what is meant by this? 10secs as previously mentioned is already on the long side.
    Despite the High Cost of Living it still remains Popular!