    Re: Large Danfoss liquid line drier
    Filter capacity over available space?
    Any details on the drier?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    58
    Posts
    1,523
    Rep Power
    35
    Maybe the last person to put the dryer on only had that one?
    Rob
  3. #3
    Join Date
    Aug 2022
    Location
    england
    Posts
    3
    Rep Power
    0
    Thanks for replying Brian, apart from Danfoss nothing legible.
  4. #4
    Join Date
    Aug 2022
    Location
    england
    Posts
    3
    Rep Power
    0
    Thanks for reply Rob, that is my assumption too but it does look like very old original equipment. I have very little experience of working on these and just wondered if I was missing something. I am rebuilding with new compressor, drier, solenoid valve, condenser fan etc. so should be good as new once flushed, thoroughly cleaned and new refrigerant. Thanks again.
  5. #5
    Join Date
    May 2012
    Location
    England
    Age
    58
    Posts
    1,523
    Rep Power
    35
    In principle fridge systems do not need a dryer.
    Why would there be a need for a filter and a dryer if the system was perfect?
    In truth the weakest link to all systems are the people who work on them and I include myself in that list
    So the dryer is there for a belt and braces backup in the event something was left inside the system that does not belong.
    Pressure drop over a good dryer is not an issue so capacity size and possibly storage is a factor?
    Is there a liquid receiver and does it have a sight glass? if yes to both then it's not storage.
    If it's capacity then somebody in the original design thought a big dryer was the way to go, all that
    means is it can take more crap from a crap system before it blocks. A smaller dryer will take less crap.
    So the real advantage of the oversized dryer will in my opinion have little effect to the operation to the system.
    Rob
  6. #6
    Join Date
    Sep 2009
    Location
    Iran
    Age
    65
    Posts
    649
    Blog Entries
    1
    Rep Power
    18
    Hi
    I think
    he used large filter instead liquid receiver plus normal filter