    Charging Process Air Conditioning



    Hi all,
    Nice to see you,

    I have a questions regarding on Air Conditioning charging process. What is the difference effect if we charge outdoor unit through Low pressure side and through high pressure side?
    any reliability issue or some safety issue may be. Please share your experienced.

    Thank you,

    Warm Regards,

    Aria



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Charging Process Air Conditioning

    Wit most modern refrigerants being charged in the liquid state care must be taken not to flood the compressor with liquid.

    It is best to charge into the liquid side as the liquid charge can be added quite quickly and therefore the majority of the charge can be added. The remaining charge can then be added carefully via the suction side with the unit running.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2011
    Location
    Tangerang
    Age
    37
    Posts
    57
    Rep Power
    14

    Re: Charging Process Air Conditioning

    Dear Brian ,

    Thank for your reply.
    But based on my trial, both of method (charge through low pressure or high pressure) , i still found unstable High Voltage test, Especially after store at warehouse for 1 dan 2 days, the ampere value was increasing. i use R-32 for refrigerant.

    Are you have experienced about that ?

    Thank You