    Carrier Aquasnap 30RA, Pro Dialog Junior



    Hello colleagues,

    Someone knows where I can change somewhere the delay time (cut in time of the compressor after reaching the set value) on a Prodialog Junior?
    If I look on a trend graph, it waits always exactly 5 minutes before restarting and I can't find this parameter.

    I used this manual https://www.manualslib.com/download/...p-30ra-Rh.html


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Carrier Aquasnap 30RA, Pro Dialog Junior

    Hi Peter

    The only thing I can find in the manual is item 3 section 4.3.11.3 - Description of the User 1 Configuration sub-menu
    This refers to delay on start up. Might be worthwhile seeing if the parameter setting is the 5 minute you have noticed

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Carrier Aquasnap 30RA, Pro Dialog Junior

    Quote Originally Posted by frank View Post
    Hi Peter

    The only thing I can find in the manual is item 3 section 4.3.11.3 - Description of the User 1 Configuration sub-menu
    This refers to delay on start up. Might be worthwhile seeing if the parameter setting is the 5 minute you have noticed
    Thanks Frank, this one was also checked.