Carrier Aquasnap 30RA, Pro Dialog Junior
Hello colleagues,
Someone knows where I can change somewhere the delay time (cut in time of the compressor after reaching the set value) on a Prodialog Junior?
If I look on a trend graph, it waits always exactly 5 minutes before restarting and I can't find this parameter.
I used this manual https://www.manualslib.com/download/...p-30ra-Rh.html
It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
-
16-07-2022, 12:56 PM #2
Re: Carrier Aquasnap 30RA, Pro Dialog Junior
Hi Peter
The only thing I can find in the manual is item 3 section 4.3.11.3 - Description of the User 1 Configuration sub-menu
This refers to delay on start up. Might be worthwhile seeing if the parameter setting is the 5 minute you have noticed
-