Thread: Carrier 30RBP
-
11-03-2022, 03:33 PM #1
Carrier 30RBP
Afternoon all,
Have an issue with a Carrier air cooled package chiller.
The fault present is a Water Loop : Delta Pressure Error.
Have spoken to Carrier and have had no luck with them advising what the issue could be.
There are two chillers, both having the same issue as they're on the same chilled water circuit.
Has anyone here come across this, and if so can you give some advise please?
TIA
-
11-03-2022, 05:01 PM #2
Re: Carrier 30RBP
It is saying that the flow rate through the machine is not within the design envelope.
See Section 9, page 35 onwards https://eto.carrier.com/litterature/...BP_160_520.pdf
-
11-03-2022, 10:12 PM #3
-
06-07-2022, 04:00 AM #4
Re: Carrier 30RBP
The flow sensors or pressure sensors clean. I have seen them block up on Geo Clima chillers, once cleaned and reading right the are fine