    Dripping water from the evaporator coil



    Hello. I have a Stulz CSD442A model 38000 kcal dual circuit air conditioner with r407 refrigerant. The problem is that it draws water drops from the evaporator and creates a water leak. No icing, no clogged drains. The air flow is created by a 5kw 3-phase motor rotating the fan. What do you think is causing the problem?



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Dripping water from the evaporator coil

    The airflow through the coil is above 2.5m/s resulting in moisture carry over.
    In cases like this you need to install moisture eliminator blades. Quite common funtion when the fan is sized too large for the coil.

  3. #3
    Join Date
    Jun 2022
    Location
    TURKEY
    Posts
    2
    Rep Power
    0

    Re: Dripping water from the evaporator coil

    could it be something else? Because there are more than one of these air conditioners and only a few of them have this problem. What kind of knives are these blades you are talking about, can you give a link?
    Thanks...

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Dripping water from the evaporator coil