    Carrier 30XA Liquid chiller Problems



    Hello,
    We have a 30XA0602 Chiller and we after starting it, there are no alarms, unit enters the normal delay sequence and after 2 minutes enters in Override sequence and does nothing. As i said there are 0 alarms.
    What this running status called "Override" means, where the problem might be? Are there some sensors/conditions that if there are not meet the Override enters?
    Thank you!



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Carrier 30XA Liquid chiller Problems

    The system could be waiting for a remote stop/start switch or similar control to be set before allowing the start sequence to continue.

    Do you have the controls manual to hand?

    try http://eto.carrier.com/lit.asp
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2022
    Location
    Romania
    Posts
    8
    Rep Power
    0

    Re: Carrier 30XA Liquid chiller Problems

    Thank you so much for the response. The system is Local ON and the remote control connection it's now disconnected but same problem. I saw on other chiller that "override" comes after the system starts and everything it's ok. Maybe it's a main board program start failure. Also if i disconnect a sensor it sees it right away. On remote BMS (building management system) i saw the chiller "Start ON" and "Pump On" but in reality it's off. I tried and replace with another main board but the controller gives me the "access denied error, connection failure". In the manual i don't see how to install a new base board ( 32GB500382EE) and how to match it with the controller (Pro dialog plus Carrier Controller).

  4. #4
    Join Date
    Jun 2022
    Location
    Romania
    Posts
    8
    Rep Power
    0

    Re: Carrier 30XA Liquid chiller Problems

    Also if i try to Service test the chiller from the main menu, it says "On" but nothing starts

  5. #5
    Join Date
    Jun 2022
    Location
    Romania
    Posts
    8
    Rep Power
    0

    Re: Carrier 30XA Liquid chiller Problems

    Carreri technician with diagnostic tool came to same conclusion as you "Waiting for an remote stop/start". But didn't know what to do next and since was just a "visit" didn't want to help us. I have all documentation but the channels for remote are disconnected, unit in Local On. And as i said before we change with a functional board from a functional chiller and had the same problem with "override".

  6. #6
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Carrier 30XA Liquid chiller Problems

    Have you tried putting a wire link into the remote stop/start terminals

  7. #7
    Join Date
    Jun 2022
    Location
    Romania
    Posts
    8
    Rep Power
    0

    Re: Carrier 30XA Liquid chiller Problems

    Yes i tried it, since i replace the MBB with a functional one from another chiller and got the same problem "Start then Override" instead of "Start, Running and then override" i really don't know what to. If i disconnect anything then the system saw it, so all the boards and sensors are checked. I will try next to measure the 24V signals on all the contactors of fans, compressors....