    AHU Design



    Hello,

    I have an AHU that we want to add extraction box above it,
    And after talking to the client we proposed to go for partial recycling system.
    and i proposed this two cases :
    Case 1 : The air recycling will be inside the AHU
    Case 2 : The air recycling will be in the duct system.
    both schematics of the propositions are in the attachements.

    For you, what's the best solution??
    Attached Images Attached Images
    • File Type: jpg 1.jpg (46.2 KB, 9 views)
    • File Type: jpg 2.jpg (59.4 KB, 6 views)



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: AHU Design

    Option 1 is the only one that will work, with option 2 there is nothing to make the recirculated air go into the AHU.

    Ensure that the recirculation and discharge air dampers are linked together on one damper motor.
    Brian - Newton Abbot, Devon, UK