    Parallel condensers



    Dear Friends,

    I have a question.

    If we have 2 air cooled condenser but sizes and capacities are different and we decide to install them parallel, As result of difference in capacity and also pressure drop, Is it necessary to use check valves at outlet of these 2 condensers in parallel ?
    I worry flow will back form condenser that has lower pressure drop to other condenser with higher pressure drop. Is this imagination true ?

    Thanks.



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Parallel condensers

    Hi
    In outlet for each one use long U legs to cover the diffrent drop pressure .
    Also your should have equalizing pipe between reciver and inlets of Condensers

  3. #3
    Join Date
    Jun 2020
    Location
    Malaysia
    Posts
    44
    Rep Power
    0

    Re: Parallel condensers

    Thanks MBC for your help

  4. #4
    Join Date
    May 2022
    Location
    Bangkok
    Posts
    1
    Rep Power
    0

    Re: Parallel condensers

    Thank you for your thread, this is extracly my question too.

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,299
    Rep Power
    31

    Re: Parallel condensers

    Quote Originally Posted by skyboy6142 View Post
    Dear Friends,<br>
    <br>
    I have a question.<br>
    <br>
    If we have 2 air cooled condenser but sizes and capacities are different and we decide to install them parallel, As result of difference in capacity and also pressure drop, Is it necessary to use check valves at outlet of these 2 condensers in parallel ?<br>
    I worry flow will back form condenser that has lower pressure drop to other condenser with higher pressure drop. Is this imagination true ?

    Thanks.
    Quote Originally Posted by mbc View Post
    Hi<br>
    In outlet for each one use long U legs to cover the diffrent drop pressure .
    Also your should have equalizing pipe between reciver and inlets of Condensers
    answer from mbc is good .... one more suggestion ...

    If you have condensers with two coils
    you need to install U-pipe (P-trap; syphon/siphon)
    on each condenser coil outlet





    The minimum recommended height of the vertical leg is
    1500 mm for ammonia. This vertical dimension h is shown in all
    evaporative condenser piping diagrams. This height is satisfactory
    for operation within reasonable ranges around normal design
    conditions and is based on the maximum condensing pressure drop
    of the coil. If service valves are installed at the coil inlets and/or outlets, the pressure drops imposed by these valves must be accounted
    for by increasing the minimum 1500 mm drop-leg height by an
    amount equal to the valve pressure drop in height of liquid refrigerant

    Best regards, Josip
    Attached Images Attached Images

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •