    Compressor false load for De-humidifier



    Hi

    I make a de-humidifier using a simple condensing unit and evaporator coil, TEV, R134A etc approx 800w cooling. The load on the machine can vary a lot and at present I fit a hot gas bypass valve (ALCO ACP3) from the discharge gas side to suction side after the TEV but before the evaporator to maintain the suction pressure above zero at low loads.
    my question is could I do this with a solenoid valve I.e. Danfoss, operated via a pressure switch? my concern is as soon as the valve opens would it let too much gas in too quickly with the pressure going up and down to quickly, I assume I could fit capillary tubing but it's knowing what size to use and would this cause any other problems?
    Any one else done this?
    My reasons are that the Alco valves are very difficult to get hold of, having to wait up to 8 weeks, so looking at an alternative.

    Regards
    CB



  2. #2
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,356
    Rep Power
    39

    Re: Compressor false load for De-humidifier

    Could try Sporlan.
    Ideally I think you need modulation type valve, not on/off, as would not be as smooth.

    https://sporlanonline.com/literature/90/90-40.pdf
    Last edited by RANGER1; 13-04-2022 at 04:59 PM.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Compressor false load for De-humidifier

    Add a crankcase pressure regulator to prevent overloading it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Compressor false load for De-humidifier

    Use either a Danfoss KVC or CPCE valve , the CPCE valve is the far superior modulating hot gas valve and allows the Tev to keep the suction superheat stable

  5. #5
    Join Date
    May 2007
    Location
    Northants
    Posts
    292
    Rep Power
    17

    Re: Compressor false load for De-humidifier

    Thanks guys !!
    re Danfoss valve it’s only a small system with 1/4” discharge pipe, smallest Danfoss valve I could see is 1/2” obviously I can add reducers but just wondering if it’ll still work ok?

  6. #6
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    453
    Rep Power
    17

    Re: Compressor false load for De-humidifier

    Would recirculating some of the warm air off the condenser back onto the evaporator during low load create an artificial load? removing the need for the hot gas bypass valve.

    Would reversing the air flow during low load be any use? Heat the intake air with the condenser then pass it through the evap, any heat rejected by the condenser could be picked up by the evap.

    If your only using the evaporator to remove moisture, and not using the condenser to then heat the dryed air. Would reducing the speed or stopping the condenser fan reduce the cooling capacity enough during low load?

    If you were to use a solenoid and pressure switch to dump hot gas into the evap, maybe a hand reg valve or needle valve could be used instead of a capiliary?
    Last edited by seanf; 16-04-2022 at 05:26 PM.

  7. #7
    Join Date
    Aug 2014
    Location
    UK
    Age
    75
    Posts
    508
    Rep Power
    25

    Re: Compressor false load for De-humidifier

    Danfoss AKV valve or an EVRP can be used for hot gas .these have small capacity and can be pulse operated over millions of cycles whereas the standard EVR solenoid valves are only rated for half a million cycles and consequently the armature and tube wears and fails very quickly if it is pulsed

  8. #8
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    867
    Rep Power
    26

    Re: Compressor false load for De-humidifier

    Not usually my type of thing.
    However I had a System I built years ago with Eutectic plates. They present a challenge as the load falls off dramatically before the plates are solidly frozen. This would lead to rapidly cycling the Compressor and slow down the cooling time.
    I used a Sporlan Hot Gas Bypass valve and it worked perfectly.
    Glenn is the one who can speak about using the larger valve of course. Hunting might be an issue.

  9. #9
    Join Date
    May 2007
    Location
    Northants
    Posts
    292
    Rep Power
    17

    Re: Compressor false load for De-humidifier

    Quote Originally Posted by Glenn Moore View Post
    Danfoss AKV valve or an EVRP can be used for hot gas .these have small capacity and can be pulse operated over millions of cycles whereas the standard EVR solenoid valves are only rated for half a million cycles and consequently the armature and tube wears and fails very quickly if it is pulsed

    that sounds a good idea, would I need a controller to control it ?

  10. #10
    Join Date
    May 2007
    Location
    Northants
    Posts
    292
    Rep Power
    17

    Re: Compressor false load for De-humidifier

    Thanks, I normally use an alco one but can’t get hold of them

  11. #11
    Join Date
    May 2007
    Location
    Northants
    Posts
    292
    Rep Power
    17

    Re: Compressor false load for De-humidifier

    Quote Originally Posted by seanf View Post
    Would recirculating some of the warm air off the condenser back onto the evaporator during low load create an artificial load? removing the need for the hot gas bypass valve.

    Would reversing the air flow during low load be any use? Heat the intake air with the condenser then pass it through the evap, any heat rejected by the condenser could be picked up by the evap.

    If your only using the evaporator to remove moisture, and not using the condenser to then heat the dryed air. Would reducing the speed or stopping the condenser fan reduce the cooling capacity enough during low load?

    If you were to use a solenoid and pressure switch to dump hot gas into the evap, maybe a hand reg valve or needle valve could be used instead of a capiliary?
    hi , thanks valve or needle valve may be a good option ����