    Jan 2015
    United Kingdom
    64
    36
    Daikin RZQ100L9V1B
    Daikin outdoor unit RZQ100L9V1B on R410A gas had circuit breaker tripped,reset and tested.
    Indoor fan works ok but outdoor unit refuses to start.240v phase and variable comms normal.
    Fuse FU6 on pcboard should be 240vac but i get 4vdc.Checked fuse for continuity and swapped
    with an identical unit but no difference.
    Compressor does not test down to earth has anyone had this fault.
    Oct 2001
    Nottingham UK
    5,668
    Re: Daikin RZQ100L9V1B
    Does it work in Emergency mode?
    Jan 2015
    United Kingdom
    64
    36
    No,nothing works.
    Oct 2001
    Nottingham UK
    5,668
    2.2 Equipment does not Operate
    Applicable Model - All models of SkyAir series
    Error Detection Method -
    Error Generating Condition -
    Supposed Causes
    Fuse blown or disorder of contact in operation circuit
    Faulty operation switch or contact point
    Faulty high pressure switch
    Faulty magnetic switch for fan motor
    Activation or fault of overcurrent relay for fan motor
    Faulty overcurrent relay for compressor
    Faulty compressor protection thermostat
    Insufficient insulation in electric system
    Faulty contact point of magnetic switch for compressor
    Malfunction of compressor
    Defective remote controller or low batteries (wireless)
    Check if address is set correctly on wireless R.C.
    Jan 2015
    United Kingdom
    64
    36
    Thanks for the info i will check this out next time i am on site.