Results 1 to 13 of 13
Thread: IOT on HVAC-R
-
21-03-2022, 02:22 PM #1
IOT on HVAC-R
Hello fellow professionals. I am an industrial refrigeration technician and automation engineer working on a company. I currently reside in Brazil and I created an IOT product for refrigeration equipment in general. It collects data from equipment in real time and sends it to a server where an AI analyzes the data and based on the experience it has created, issues a fault diagnosis. Currently it has been working well in split, self and rooftop equipment. And now I want to move it to chillers, which creates a new scenario for me in which chillers have more complex behaviors and a variety of equipment configurations. Whoever is interested in the project and wants to discuss it or likes IOT I am open to hear tips and criticisms.
Big hug to all.
Data on the project:
Resume:
The hardware monitors variables such as temperature, current and voltage of the equipment, sends the data over the internet (WIFI) where the AI issues a diagnosis with 80% accuracy and 7 days in advance through a mobile APP.
How long to install: 3 hours on average
How many sensors: 7
Consume of data: 1mb hour.
Sem título.jpg
-
16-08-2022, 07:41 PM #2
Re: IOT on HVAC-R
ok... I know this is a spam thread....
but if anyone is interested in this stuff just ask some questions, I'm running an esp32 board (same family as the picture above) and have 20 temp sensors connected to it reporting back via wifi
I'm about to add current and power sensors to it
pressure sensors look easy but I don't think I'll bother
board plus temp sensors set me back about £20
-
16-08-2022, 11:55 PM #3
Re: IOT on HVAC-R
That looks like a useful piece of kit and at that price it's got to be worth a try.
Edit: not actually designed as a spam thread but our Josip got hacked and was being used by some oik from far off lands.Last edited by Brian_UK; 16-08-2022 at 11:57 PM.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
21-08-2022, 08:35 PM #4
Re: IOT on HVAC-R
no brainer at that price @knighty, fair play to you for getting it set up. Would you have any guidance/advice for someone not too proficient with this stuff for doing what you have put together?
Mostly found in the southern part of this green and pleasant land.
-
21-08-2022, 11:55 PM #5
Re: IOT on HVAC-R
I bought some ESP32 boards like these...
https://www.ebay.co.uk/itm/304561797507
temperature sensors like these...
https://www.ebay.co.uk/itm/111434870374
and isolation boards like these
https://www.ebay.co.uk/itm/362990277340
easier than me writing it up, here's an online guide
https://randomnerdtutorials.com/esp8...h-arduino-ide/
I haven't added the mains power boards yet, I'll come back and update tis when I have
the temperature sensors are really cool, they have a chip in them which can talk to the ESP32 board, so you wire all the temp sensors in parallel.... negative wire, 5v wire (to the 5v on the board) and a daa wire (all data wires joined together)
-
23-08-2022, 10:11 AM #6
Re: IOT on HVAC-R
.. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..
-
25-08-2022, 10:01 PM #7
Re: IOT on HVAC-R
it's all open source, so you can do (pretty much) whatever you like with it
lots of the expensive systems that you see are based on the same board and sensors
there's loads of options for the controller boards... they can do all sorts, and they're used in all sorts of things already - I have LED colour changing bulbs which are based on the same system
-
26-08-2022, 06:45 PM #8
Re: IOT on HVAC-R
bit of an odd one here.... I'm setup reading evap temp, air in temp and air out temp...
but there's hardly any difference between air in and out temp?
one freezer right now says...
-20.9'C evap temp
-15.1'C air in temp
-15.3'C air out temp
used as a blast freezer so -20evap and -15 air in sounds about right to me?
am I using the wrong type of temp sensors? https://www.ebay.co.uk/itm/111434870374
I'll pull all 3 temp sensors and drop them into a cup of water to calibrate them, make sure they're all reading right.... but I had 10 running on the bench and they were all within 0.5'C on the bench - I took that as fine because they were spread out a bit etc..
there's plenty of evap airflow there
condenser is tossing out plenty of heat
-
28-08-2022, 03:56 PM #9
Re: IOT on HVAC-R
If it's a blast freezer, small compartment? If so may need warm product in place to see wider delta T
Mostly found in the southern part of this green and pleasant land.
-
31-08-2022, 12:42 PM #10
Re: IOT on HVAC-R
box is the box from the back of a truck, 27ft long 8ft wide, about 8ft high
evaps are standard freezer evaps - calling it a blast freezer is using a bit of poetic licence :-o
it's nice to see graphs of what's going on.... here's air on / evap / air off temp probes for 2 boxes yesterday
Untitled.png
Untitled2.png
one freezer made it down to set point so you can see it cycle on and off, other one never got that low
I think my evap probs are badly places... too close to the incoming air so that's throwing the reading off?
I need to add an extra temp prob at the other end of the box to use as room temp - or at least a probe somewhere out of the airflow
graphs/numbers etc/ will really help me trouble shoot problems in the future and find them before they cause trouble
colour changing bulb is up and running.... but different shades of blue are too hard to tell apart... I'll change it to stick with full colours and change colour instead, so red/yellow/orange/blue/green
-
31-08-2022, 02:42 PM #11
Re: IOT on HVAC-R
Any ice on the evap coil? front face, back face, inside the coil.
All the fans running, and blowing air in the right direction?
Suction superheat ok?
-
31-08-2022, 05:30 PM #12
Re: IOT on HVAC-R
everything is running great, good airflow, no ice build up
just the evap probs are reading too high, I think they're too far on the incoming air side, so that incoming air is throwing the reading off
it doesn't really matter, I'll push them in a bit further, they're only for a rough guide
could always fix them to the a coper pipe at the end of the evap instead
-
31-08-2022, 09:16 PM #13
Re: IOT on HVAC-R
How do your temp readings compare to a normal thermometer reading ?