    Drier then site glass why?



    I have always installed the site glass after the drier.This way round the site glass may show short of gas when the drier is blocked.This can catch out the less experienced engineer.Why is it fitted this way round?



  2. #2
    Join Date
    Nov 2005
    Location
    Southampton
    Age
    46
    Posts
    54
    Rep Power
    19

    Re: Drier then site glass why?

    sightglass usually has moisture indicator on it , so shows that drier is working and is absorbing moisture!!

  3. #3
    Join Date
    Oct 2002
    Location
    australia
    Posts
    28
    Rep Power
    0

    Re: Drier then site glass why?

    Quote Originally Posted by aeb200
    sightglass usually has moisture indicator on it , so shows that drier is working and is absorbing moisture!!
    i've had a system at 500 micron after performing a triple evacuation and the moisture indicator still showed wet, so i wouldn't really trust them

  4. #4
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Drier then site glass why?

    If you install the sight glass after the drier it will always remain nice and clear to look through.

  5. #5
    Join Date
    Jun 2005
    Location
    S****horpe
    Age
    52
    Posts
    135
    Rep Power
    20

    Re: Drier then site glass why?

    Presumably if the drier blocked you wouldn't know about it? The expansion valve would fully open but you'd get boiling in the line before the valve. The sight glass before the drier would still be flooded with liquid though.
    It's a lovely day to pump some gas

  6. #6
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: Drier then site glass why?

    normaly the the drier gets cold and sweaty as its restricting,this carries on upto the valve as it does not have a adiquate supply of liquid,you tend to see half a glass or so sitting in the bottom,thats the reason for putting it that way round,not always the case but common.

  7. #7
    Join Date
    May 2005
    Location
    Minnesota
    Age
    52
    Posts
    19
    Rep Power
    0

    Re: Drier then site glass why?

    Sight glass placement after the dryer provides more useful information to the service tech.

    As far as the moisture indicators go, I don't trust them either.

  8. #8
    Join Date
    Aug 2006
    Location
    Ireland
    Age
    47
    Posts
    26
    Rep Power
    0

    Re: Drier then site glass why?

    Having your sight glass fitted to your liquid line after your drier will show you if your drier is partially blocked. If your sight glass is showing a lack of refrigerant yet your receiver is full (going on bottom sight glass) then you should replace your drier.

    The other way of telling if your drier is partially blocked, is you’ll notice a temperature difference across the drier. Liquid line tends to be warmer before the drier that after.

Similar Threads

  1. liquid line sight glass mystery
    By austech in forum Technical Discussions
    Replies: 19
    Last Post: 18-07-2006, 08:16 PM
  2. Sight Glass Located
    By Abe in forum Trouble Shooting
    Replies: 3
    Last Post: 22-01-2002, 01:22 AM
  3. Shelf life of an uncapped dessicant drier.
    By eberg in forum Air Conditioning
    Replies: 2
    Last Post: 22-08-2001, 01:22 PM
  4. Sight Glass,
    By Abe in forum Trouble Shooting
    Replies: 4
    Last Post: 03-08-2001, 08:36 PM
  5. Drier Position
    By subzero*psia in forum Commercial
    Replies: 8
    Last Post: 23-07-2001, 10:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •