Results 1 to 8 of 8
Thread: Drier then site glass why?
Hybrid View
-
26-06-2006, 09:16 PM #1
Drier then site glass why?
I have always installed the site glass after the drier.This way round the site glass may show short of gas when the drier is blocked.This can catch out the less experienced engineer.Why is it fitted this way round?
-
26-06-2006, 09:47 PM #2
Re: Drier then site glass why?
sightglass usually has moisture indicator on it , so shows that drier is working and is absorbing moisture!!
-
27-06-2006, 08:03 AM #3
Re: Drier then site glass why?
Originally Posted by aeb200
-
27-06-2006, 12:03 PM #4
Re: Drier then site glass why?
If you install the sight glass after the drier it will always remain nice and clear to look through.
-
27-06-2006, 12:39 PM #5
Re: Drier then site glass why?
Presumably if the drier blocked you wouldn't know about it? The expansion valve would fully open but you'd get boiling in the line before the valve. The sight glass before the drier would still be flooded with liquid though.
It's a lovely day to pump some gas
-
28-06-2006, 07:59 AM #6
Re: Drier then site glass why?
normaly the the drier gets cold and sweaty as its restricting,this carries on upto the valve as it does not have a adiquate supply of liquid,you tend to see half a glass or so sitting in the bottom,thats the reason for putting it that way round,not always the case but common.
-
31-07-2006, 05:24 AM #7
Re: Drier then site glass why?
Sight glass placement after the dryer provides more useful information to the service tech.
As far as the moisture indicators go, I don't trust them either.
-
15-09-2006, 09:59 PM #8
Re: Drier then site glass why?
Having your sight glass fitted to your liquid line after your drier will show you if your drier is partially blocked. If your sight glass is showing a lack of refrigerant yet your receiver is full (going on bottom sight glass) then you should replace your drier.
The other way of telling if your drier is partially blocked, is you’ll notice a temperature difference across the drier. Liquid line tends to be warmer before the drier that after.
Similar Threads
-
liquid line sight glass mystery
By austech in forum Technical DiscussionsReplies: 19Last Post: 18-07-2006, 08:16 PM -
Sight Glass Located
By Abe in forum Trouble ShootingReplies: 3Last Post: 22-01-2002, 01:22 AM -
Shelf life of an uncapped dessicant drier.
By eberg in forum Air ConditioningReplies: 2Last Post: 22-08-2001, 01:22 PM -
Sight Glass,
By Abe in forum Trouble ShootingReplies: 4Last Post: 03-08-2001, 08:36 PM -
Drier Position
By subzero*psia in forum CommercialReplies: 8Last Post: 23-07-2001, 10:28 PM