    Apr 2006
    77
    Drier then site glass why?
    I have always installed the site glass after the drier.This way round the site glass may show short of gas when the drier is blocked.This can catch out the less experienced engineer.Why is it fitted this way round?
    Nov 2005
    Southampton
    54
    Re: Drier then site glass why?
    sightglass usually has moisture indicator on it , so shows that drier is working and is absorbing moisture!!
    Oct 2002
    28
    Quote Originally Posted by aeb200
    i've had a system at 500 micron after performing a triple evacuation and the moisture indicator still showed wet, so i wouldn't really trust them
    Dec 2004
    Australia
    52
    519
    If you install the sight glass after the drier it will always remain nice and clear to look through.
    Jun 2005
    S****horpe
    135
    Presumably if the drier blocked you wouldn't know about it? The expansion valve would fully open but you'd get boiling in the line before the valve. The sight glass before the drier would still be flooded with liquid though.
    It's a lovely day to pump some gas
    Feb 2006
    derbyshire
    610
    normaly the the drier gets cold and sweaty as its restricting,this carries on upto the valve as it does not have a adiquate supply of liquid,you tend to see half a glass or so sitting in the bottom,thats the reason for putting it that way round,not always the case but common.
    May 2005
    Minnesota
    52
    Sight glass placement after the dryer provides more useful information to the service tech.
    As far as the moisture indicators go, I don't trust them either.
    Ireland
    Having your sight glass fitted to your liquid line after your drier will show you if your drier is partially blocked. If your sight glass is showing a lack of refrigerant yet your receiver is full (going on bottom sight glass) then you should replace your drier.
    The other way of telling if your drier is partially blocked, is you’ll notice a temperature difference across the drier. Liquid line tends to be warmer before the drier that after.
  1. liquid line sight glass mystery
    By austech in forum Technical Discussions
    Last Post: 18-07-2006, 08:16 PM
  2. Sight Glass Located
    By Abe in forum Trouble Shooting
    Last Post: 22-01-2002, 01:22 AM
  3. Shelf life of an uncapped dessicant drier.
    By eberg in forum Air Conditioning
    Last Post: 22-08-2001, 01:22 PM
  4. Sight Glass,
    Last Post: 03-08-2001, 08:36 PM
  5. Drier Position
    By subzero*psia in forum Commercial
    Last Post: 23-07-2001, 10:28 PM