Results 1 to 27 of 27

Thread: heat exchanger

  1. #1
    Join Date
    Sep 2005
    Location
    UK
    Age
    42
    Posts
    191
    Rep Power
    20

    heat exchanger



    hi

    long story short, I own a small frozen dog food factory, and with the hot weather coming back again freezing everything we need to freeze is becoming a problem (up to 4,000lb of meat needs to freeze overnight)

    I'd like to help the condensers out a bit by cooling the hot liquid just before it enters the freezer room with cold water....

    does anyone know where I can buy a heat exchanger to do this ?

    I *think* the tubing is 15mil going in and 22mil coming out thanks

    Alan.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: heat exchanger

    Hi Knighty, welcome back, how's the leg?

    Before we start remodelling you system again, did you get it up and running as you wanted last year?

    A quick fix right now would be to run a water hose with a spray head and point it at the condenser coils; don't spray at full force a gentle spray will suffice.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2006
    Location
    scotland
    Posts
    5
    Rep Power
    0

    Re: heat exchanger

    Quote Originally Posted by Brian_UK
    Hi Knighty, welcome back, how's the leg?

    Before we start remodelling you system again, did you get it up and running as you wanted last year?

    A quick fix right now would be to run a water hose with a spray head and point it at the condenser coils; don't spray at full force a gentle spray will suffice.
    leave it to the pros what you are conserding doing is just nonsence

  4. #4
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: heat exchanger

    does anyone know where I can buy a heat exchanger to do this ?

    Yes.


    I *think* the tubing is 15mil going in and 22mil coming out thanks

    Take it from me, it is not 15 and 22 mm.


    leave it to the pros what you are conserding doing is just nonsence

    Agreed.
    Takes a licking, keeps on ticking.

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: heat exchanger

    Quote Originally Posted by not tamed
    leave it to the pros what you are conserding doing is just nonsence
    Hi not tamed and welcome to the forum, a little bit of history about yourself as way of introduction would be of interest to us all.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: heat exchanger

    Not tamed, - what a name - seems your just in the business and missing some, no.. a lot of experience.
    Done this hundred times, even today, 3 times with a very good result.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: heat exchanger

    Quote Originally Posted by Brian_UK

    A quick fix right now would be to run a water hose with a spray head and point it at the condenser coils; don't spray at full force a gentle spray will suffice.
    Brian did only say a quick fix......

    Not a long term solution.

    I worked on a supermarket where the owner hooked up a sprinkler to every unit. When the weather got over 30 deg C he would turn on this system.

    The gear serving the supermarket was in pretty poor condition(Probably due to water being sprayed on it).But without doing this on some hot days it would stop running.

    BTW I am not recommending this practice.

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: heat exchanger

    I don't recommend it long term but sometimes it's all you can do with the kit that has been installed.

    Some customers will just NOT spend the money or, also relevant, they cannot afford the upgrade yet.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Feb 2006
    Location
    derbyshire
    Posts
    610
    Rep Power
    19

    Re: heat exchanger

    the units obviously flat out,jet wash the condenser,[remove the fan assy first] thats your starting point !, is there a siting problem with venilation !, maybe look to getting hold of a remote condenser as a cheaper solution.

  10. #10
    Join Date
    Sep 2005
    Location
    UK
    Age
    42
    Posts
    191
    Rep Power
    20

    Re: heat exchanger

    Quote Originally Posted by Brian_UK
    Hi Knighty, welcome back, how's the leg?
    Before we start remodelling you system again, did you get it up and running as you wanted last year?
    A quick fix right now would be to run a water hose with a spray head and point it at the condenser coils; don't spray at full force a gentle spray will suffice.
    wow you must have a good memory !

    my leg's much better now thanks, I'm pretty much back to normal

    last year... I ended up buying an extra freezer room so I can leave stock flat packed on trays for longer before its packed into boxes.. it was a temporary fix and I was hoping to have something more permanent by now.... things are so busy at the moment that if it doesn't absolutely have to be done right away, then its not

    I've steam cleaned through the condenser coils already and air flow is good, I thought about having a small spray of water over the condensor.... but I'm worried about the problems caused by the water (corrosion etc..)

  11. #11
    Join Date
    Sep 2005
    Location
    UK
    Age
    42
    Posts
    191
    Rep Power
    20

    Re: heat exchanger

    and now for an update... after a check today, the freezer was still struggling to keep the temp down and get everything frozen... the high pressure (liquid) line coming out of the compressor was very hot, too hot to touch, but by the time the liquid was re-entering the fridge it was pretty well cooled down, so I'm thinking the water cooling might not be enough, and I'd rather go for a longer term system. (spreading products out around numerous freezers is a pain and time taking)

    but.... I do have a couple of spare hardly used full system's that I picked up cheap when a local factory closed down... If I find the spec. of those compressors, and for the compressor I'm using for my main fridge would you guys be able to point me to an expansion valve and pro. heat exchanger to link the 2 up ? (having the smaller compressor cooling the liquid before it enters the fridge) ?

    I'm friends with a local refrigeration engineer who could hook it all up for me, and I could wire it in myself no problems

  12. #12
    Join Date
    Sep 2005
    Location
    UK
    Age
    42
    Posts
    191
    Rep Power
    20

    Re: heat exchanger

    p.s. the cheaper the better

    edit:

    the main freezer is running on 404a (I'll double check that tho)

    what kind of temp can I go down to with 404a without any problems ? (oil freezing etc..)

    I don't really need to be any colder, just need to keep the temp down and to bring it down quicker... the freezer normally runs at -18'C but I've set it to -23'C at the moment (as low as it will go)

    I'm not sure if it will ever make it down to -23, but every degree helps in with this weather !
    Last edited by knighty; 13-07-2006 at 03:40 AM.

  13. #13
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: heat exchanger

    What I would sujest is switching to a better gas then over sizing your condencer system a bit, that will assist in sub cooling and lower the head pressures and temps, providing there is a beter suited replacment, but in either case putting in a larger Condenser will help I do think.

  14. #14
    Join Date
    Sep 2005
    Location
    UK
    Age
    42
    Posts
    191
    Rep Power
    20

    Re: heat exchanger

    mm, can you point me to a better gas ?

    I've searched these forums, but theres so much information, and a lot of it is gobildygook to me

    the idea behind the heat exchanger is, I could add a lot of cooling capacity to the system for relativly little money... (with water all i need is the heat exchanger and pump, using a second compressor all i need is the heat exchanger and a expansion valve for it)

    thanks

    Alan.

  15. #15
    Join Date
    Apr 2006
    Location
    Not so sunny coast (BC Canada)
    Age
    41
    Posts
    1,620
    Rep Power
    24

    Re: heat exchanger

    Hmmm Could get a 20 plat heat exchanger low profile and high performance.

    Find a gas with the same low temp but with lower head pressures.

  16. #16
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: heat exchanger

    Quote Originally Posted by knighty
    the high pressure (liquid) line coming out of the compressor was very hot, too hot to touch...
    The hot line coming out of the compressor is the discharge gas line, not the liquid line. The liquid line is the pipe that comes out of the condenser.

    If you want to pick up a lot of cooling capacity, install a small brazed plate heat exchanger (BPHE) in the liquid line (downstream of the receiver). Use a little refrigeration system to cool the BPHE. Now you have an instant mechanical subcooler.

    Of course it all has to be sized correctly to operate properly.

    Changing the gas is too much like playing around with the system until you get a favorable result. I would not recommend this.

    This subcooling system should start when the main refrigeration system starts, and shut off when the main refrigeration system stops.
    Last edited by US Iceman; 29-07-2006 at 03:22 PM.

  17. #17
    Join Date
    Aug 2006
    Location
    China
    Posts
    15
    Rep Power
    0

    Re: heat exchanger

    good idea,

  18. #18
    Join Date
    Dec 2005
    Location
    Zagreb
    Posts
    190
    Rep Power
    19

    Exclamation Re: heat exchanger

    Ad air cooled condenser in parallel with old one.Fit the solenoid valve on new condenser inlet.Dgust you need to fit the right size condenser.

    Renato

  19. #19
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: heat exchanger

    I fully agree with US Iceman. He has given a very effective solution, but you have to do the proper selection of the subcooling system. Even Brians idea of spraying a small amount of water over the condenser is good, but should be done for a short while till you adopt Icemans views. Why not try for a day and see the changes it brings. I have done it a number of times and the results were good. However finally you have to change your condenser to match the total heat rejection of the compressor. Both the ideas are good.

    Samarjit Sen

  20. #20
    Join Date
    Aug 2006
    Location
    China
    Posts
    15
    Rep Power
    0

    Talking Re: heat exchanger

    does anyone know where I can buy a heat exchanger to do this ?

    I *think* the tubing is 15mil going in and 22mil coming out thanks

    Alan.[/quote]

    You know, it is not just providing equipments, also a cooling solution, you can contact me

  21. #21
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: heat exchanger

    Quote Originally Posted by The MG Pony View Post
    What I would sujest is switching to a better gas then over sizing your condencer system a bit, that will assist in sub cooling and lower the head pressures and temps, providing there is a beter suited replacment, but in either case putting in a larger Condenser will help I do think.
    Changing to a gas with a much lower HP will give you a lot less cooling capacity.
    This isn't the proper way to solve this.
    There's basically something wrong and this must be changed/improved.
    Last edited by Peter_1; 09-09-2006 at 12:22 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  22. #22
    Join Date
    May 2006
    Location
    India
    Age
    82
    Posts
    1,013
    Rep Power
    19

    Re: heat exchanger

    Changing refrigerant would reduce the capacity as has been rightly said by Peter 1. Some years ago I had read in a Searle catalogue, that by installing a heat exchanger of the type suction/ liquid in the discharge pipe line before the condenser, and passing water through it so as to cool the discharge line, one can attain a much better condensation. I had done the same on a couple of plants and had found these to be very effective. Maybe you can try the same.

  23. #23
    Join Date
    Sep 2005
    Location
    UK
    Age
    42
    Posts
    191
    Rep Power
    20

    Re: heat exchanger

    well... as a temporary meausure I added the most powerfull fan ever imagined hanghing infront of the condensor.. sounds like a jet engine and I can't run it during the day because its too noisy..... just waiting for the electric bill now

    but... I'm in the middle of sourcing a heat exchanger I can run water through to use as a more permenant solution.... which should be cheaper than runing 2 units :-)

    spending about £200 a week on electric as it is (about $370)

  24. #24
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: heat exchanger

    knighty,

    You are spending a lot of money for questionable results.

    spending about £200 a week
    If you can afford several months of this additional cost, you can afford to pay a good refrigeration person to fix your problems.

    Several months of this expenditure would probably pay for the separate subcooling system. Then you can concentrate on the condenser problem, maybe?

  25. #25
    Join Date
    Sep 2005
    Location
    UK
    Age
    42
    Posts
    191
    Rep Power
    20

    Re: heat exchanger

    sorry, I should have said, that;s the total electric bill for the company, not just the extra fan !

    tho most of that bill will be for the fridges/freezers... the rest will just be for lights, we have a few big machines but they don;t run for that long.

  26. #26
    Join Date
    Sep 2006
    Location
    u.k.
    Age
    44
    Posts
    6
    Rep Power
    0

    Re: heat exchanger

    Hi
    Heres the bush mechanic method of head pressure control for air cooled condensors.

    Equipment needed:
    1.) Automatic garden sprayers, associated piping, fittings and water solenoid valve.
    2.) Automatic reset discharge pressure switch or suitable thermostat to monitor liquid line temprature.

    Method :
    1.)Mount the sprayers under the condensor, i hope the fan motors are waterproof.
    2.)Use the pressure switch to switch the sprayers on when the head pressure gets to high and off when it gets too low.
    Or use the thermostat to monitor the liquid line temprature.

    This is not the way to do it, rather get a condensor thats properly sized for your maximum ambient conditions.

    Hope you get it right.

  27. #27
    Join Date
    Jul 2006
    Location
    New Berlin, Wisconsin, USA
    Age
    65
    Posts
    57
    Rep Power
    18

    Re: heat exchanger

    Be careful about spraying water on condenser coils, depending on the hardness of the water you would not only have corrosion, but also calcium build up and it may end up lowering the efficiency of the coils in the long run. You are essentially making an evaporative condenser, but when you start to evaporate the water the residual minerals and salts that are present in the water are left behind. In evaporative condensers the water is recycled and it is monitered and treated to prevent the accumulation of mineral deposits and salts that are present in the water.

Similar Threads

  1. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  2. Liquid reciever w/spiral heat exchanger
    By Carlo Hansen in forum Fundamentals
    Replies: 10
    Last Post: 16-06-2006, 01:18 PM
  3. heat exchanger design
    By Lc_shi in forum Fundamentals
    Replies: 33
    Last Post: 13-03-2006, 09:57 AM
  4. R134a <-> liquid heat exchanger design
    By DaBit in forum Technical Speculations
    Replies: 19
    Last Post: 10-05-2002, 08:36 AM
  5. Restricted Heat Exchanger
    By Abe in forum Trouble Shooting
    Replies: 1
    Last Post: 28-10-2001, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •