    Hi,

    Recently installed a York YMPA0100 AMICHI unit for brine purposes only...
    Is there a cheap/easy solutions for using a plain switch to use two setpoints?
    During the day we need two different setpoints (-10°C and 0°C).
    The operators simply want to use a toggle switch to change the setpoint...


    Could this be done without a BacNet / Modbus unit?
    I'm not familiar with this kind of protocols...



    Thanks in advance,
    Have a great weekend!



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: YORK YMPA0100 AMICHI - BACnet / Modbus

    Hi
    Put 2 thermostats with 2 set point
    Then put one key 1-0-2
    Thermostat 1 comes to 1
    Thermostat 2 comes to 2
    From Common goes to your system