    Vilter VSS1851 capacity calculation



    Hello,

    Is there somebody abble to select a Vilter single screw compressor (software required).
    I'm in need of capacity and schaft power consumption at the following conditions:

    • Compressor type Vilter VSS 1851
    • Refrigerant ammonia
    • Revolution 3000 rpm
    • Saturated suction temperature -44,07°C => -47,3°F
    • Suction non usefull superheat 4°K => 7,2°F




    • Saturated discharge temperature +27,7°C =>81,9°F



    • Liquid subcooling 2°K =>3,6°F



    • Non economized


    many thanks



  2. #2
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Vilter VSS1851 capacity calculation

    Hi, cricri,


    found this maybe can be of some help to you ...


    https://climate.emerson.com/en-sg/to...ction-software


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  3. #3
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: Vilter VSS1851 capacity calculation

    Thanks Josip, but no calculation possibility with this link.
    They don't want to share their Soft, Probably the end of my professional Email address frighten them...

  4. #4
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Vilter VSS1851 capacity calculation

    Hi, cricri

    cannot promise anything,
    but I can ask one of my friend for help.

    Not sure, but I believe they have Vilter software.
    I can ask him tomorrow.

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  5. #5
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19

    Re: Vilter VSS1851 capacity calculation

    Thank you Josip,
    I forgot to mention that oil cooling is liquid; (éthylène glycol)

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Vilter VSS1851 capacity calculation

    Hi, cricri ...

    check your email ...

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •