    Dear Friends,
    Would you please help me to understand reason of this installation ? "Installing a check valve beside of a ball valve" for why ?
    See my photo.
    Thanks.
    11,025
    Re: Check valve
    Possibly to relieve any overpressure that may occur within the section that could be valved off but still contains liquid.
    Sep 2009
    Iran
    66
    672
    1
    Re: Check valve
    it is check valve .
    when you want to replace core inside filter you close inlet valve and outlet valve in filter.
    then you pour hot water on core dryer .
    all liquid comes to gas and goes back by check valve to condenser side ,so you save a lots of refrigerant liquid
    Norway
    1,036
    4
    Re: Check valve
    it is check valve .
    Agree with mbc.
    would be useful for isolating and pumping down the filter by adding hot water, or simply as a safety against trapped liquid.
    On our ammonia plants we use 1 bar safety/check valves on all parts where you may get trapped liquid when you close it for service.
    -Cheers-
    Tycho
    Jun 2020
    Malaysia
    44
    Re: Check valve
    it is check valve .
    Thanks my friend.
    Jun 2020
    Malaysia
    44
    Re: Check valve
    Agree with mbc.
    Thanks a lot.
    Jul 2022
    India
    2
    Re: Check valve
    Hi bro, When you want to replace core inside filter you close inlet valve and outlet valve in filter. then you pour hot water on core dryer . all liquid comes to gas and goes back by check valve to condenser side ,so you save a lots of refrigerant liquid.