Results 1 to 7 of 7

Thread: Check valve

  1. #1
    Join Date
    Jun 2020
    Location
    Malaysia
    Posts
    44
    Rep Power
    0

    Check valve



    Dear Friends,
    Would you please help me to understand reason of this installation ? "Installing a check valve beside of a ball valve" for why ?

    See my photo.

    Thanks.


    index.jpg



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Check valve

    Possibly to relieve any overpressure that may occur within the section that could be valved off but still contains liquid.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Check valve

    Hi

    it is check valve .
    when you want to replace core inside filter you close inlet valve and outlet valve in filter.
    then you pour hot water on core dryer .
    all liquid comes to gas and goes back by check valve to condenser side ,so you save a lots of refrigerant liquid

  4. #4
    Join Date
    Jan 2006
    Location
    Norway
    Posts
    1,035
    Blog Entries
    4
    Rep Power
    31

    Re: Check valve

    Quote Originally Posted by mbc View Post
    Hi

    it is check valve .
    when you want to replace core inside filter you close inlet valve and outlet valve in filter.
    then you pour hot water on core dryer .
    all liquid comes to gas and goes back by check valve to condenser side ,so you save a lots of refrigerant liquid
    Agree with mbc.

    would be useful for isolating and pumping down the filter by adding hot water, or simply as a safety against trapped liquid.

    On our ammonia plants we use 1 bar safety/check valves on all parts where you may get trapped liquid when you close it for service.
    -Cheers-

    Tycho

  5. #5
    Join Date
    Jun 2020
    Location
    Malaysia
    Posts
    44
    Rep Power
    0

    Re: Check valve

    Quote Originally Posted by mbc View Post
    Hi

    it is check valve .
    when you want to replace core inside filter you close inlet valve and outlet valve in filter.
    then you pour hot water on core dryer .
    all liquid comes to gas and goes back by check valve to condenser side ,so you save a lots of refrigerant liquid
    Thanks my friend.

  6. #6
    Join Date
    Jun 2020
    Location
    Malaysia
    Posts
    44
    Rep Power
    0

    Re: Check valve

    Quote Originally Posted by Tycho View Post
    Agree with mbc.

    would be useful for isolating and pumping down the filter by adding hot water, or simply as a safety against trapped liquid.

    On our ammonia plants we use 1 bar safety/check valves on all parts where you may get trapped liquid when you close it for service.
    Thanks a lot.

  7. #7
    Join Date
    Jul 2022
    Location
    India
    Posts
    2
    Rep Power
    0

    Re: Check valve

    Hi bro, When you want to replace core inside filter you close inlet valve and outlet valve in filter. then you pour hot water on core dryer . all liquid comes to gas and goes back by check valve to condenser side ,so you save a lots of refrigerant liquid.
    Regards
    Tigur 16