    Chiller pump down



    We are servicing a couple of glycol chillers with R404A. One of them randomly pumps-down at start up. There´s a solenoid valve (Emerson 240RA9T7T 7/8") and a TCLE thermOstatic expansion valve.

    All works well except sometimes during start up the chiller pumps down, actually due to the Low Pressure delay, the chiller stops when pressure goes down to 0 bar.

    We are wondering what might be the cause. Is it ok to assume a malfunctioning thermostatic valve can not be the cause because pressure goes really low ? In that case, what may cause a random solenoid valve functioning ?



  2. #2
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: Chiller pump down

    Is there a low pressure bypass timer at start up ?

  3. #3
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    452
    Rep Power
    17

    Re: Chiller pump down

    Whats the ambient temp, gycol temp on start up, and is the thermostatic valve covered in ice when it faults on starting up?

  4. #4
    Join Date
    Aug 2005
    Location
    ARGENTINA
    Age
    59
    Posts
    26
    Rep Power
    0

    Re: Chiller pump down

    Is there a low pressure bypass timer at start up ?

    Yes. It is set it for about 20 seconds. This is why pressure goes so low sometimes.
    Last edited by otrotabi; 21-01-2022 at 11:49 AM.

  5. #5
    Join Date
    Aug 2005
    Location
    ARGENTINA
    Age
    59
    Posts
    26
    Rep Power
    0

    Re: Chiller pump down

    It´s hot here now, about 35 to 40 Celsius. Chillers start when glycol temp is -3º and stop when they get to -5º.

    No, there´s no ice on the thermostatic valve that I was able to notice.

    However my main question is: is it possible for a thermostatic valve to close liquid line 100%, causing pump down ? I know electronic valves can do it, but mechanical valves are not meant to do that, but I wonder if soemthing goes wrong with the orifice that could be the case.

    We have already replaced thermostatic element (basically because it is far easier to do than replacing the solenoid valve) but I am wondering whether we just lost some time doing that.
    Last edited by otrotabi; 21-01-2022 at 11:56 AM.

  6. #6
    Join Date
    Aug 2005
    Location
    ARGENTINA
    Age
    59
    Posts
    26
    Rep Power
    0

    Re: Chiller pump down

    So, as a follow up for this topic, I found this article: https://blog.parker.com/site/usa/en-...noid-valves-us where it states that : Grossly oversized valve which will not have the minimum 1 psi pressure drop and its disc/piston/diaphragm will NOT return to its normal position.

    However in this case, normal position is closed and the valve does close, the problem is it will not open. From an analysis of how these kind of valves work, an oversized valve would probably not close properly, but is should open.

    Are we wrong in our undestanding ?

  7. #7
    Join Date
    Oct 2009
    Location
    england
    Age
    77
    Posts
    243
    Rep Power
    19

    Re: Chiller pump down

    Is the solenoid valve energised ?
    Is it energised when the compressor starts or before ?
    Daft question is it in the right way round ?

  8. #8
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Chiller pump down

    Hi Otrotarbi.
    I may be completely off track.
    What model do you have please?
    I would be checking the Glycol flow circuit for restrictions. if Not!
    Is there anything else that could cause a Suction Pressure drop?
    Basically i am intrigued to know what chiller System you have.
    Good luck grizzly
    Last edited by Grizzly; 21-01-2022 at 07:44 PM.
    Despite the High Cost of Living it still remains Popular!

  9. #9
    Join Date
    Aug 2005
    Location
    ARGENTINA
    Age
    59
    Posts
    26
    Rep Power
    0

    Re: Chiller pump down

    Quote Originally Posted by redroge View Post
    Is the solenoid valve energised ?
    Is it energised when the compressor starts or before ?
    Daft question is it in the right way round ?
    The chiller does work. Sometimes the symptoms I describe happen. Yes, I checked the electrical circuit and evetyting seems normal.

  10. #10
    Join Date
    Aug 2005
    Location
    ARGENTINA
    Age
    59
    Posts
    26
    Rep Power
    0

    Re: Chiller pump down

    Quote Originally Posted by Grizzly View Post
    Hi Otrotarbi.
    I may be completely off track.
    What model do you have please?
    I would be checking the Glycol flow circuit for restrictions. if Not!
    Is there anything else that could cause a Suction Pressure drop?
    Basically i am intrigued to know what chiller System you have.
    Good luck grizzly
    Yes, we did check glycol flow, there are two different flow switches on the circuit so no flow seems to be out of the question.

    They are custom made industrial chillers with everything brand new. S&T heat exchanger, Copeland Discus compressor and it works 9 times out of 10 starts. It is a little puzzling the way the liquid solenoid valve behaves anyway. We will remove the solenoid piston next time, there is a big suction accumulator on the circuit so there is no actual risk of liquid floodback. Images allowed in this forum need to be small, but maybe you can get an idea of what it looks like.


    chiller.png