    Post Daikin 51e/140



    Hello guys

    iam new here, we have problem whit: A3 Malfunction of drain level control system.
    this came after change of indoor module.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin 51e/140

    Check that the drain level sensor is connected correctly to the new pcb board.
    Look for the wiring diagram on the inside of the indoor electrical cover and it will reference the sensor wiring and the X?? connector on the pcb

  3. #3
    Join Date
    Jan 2022
    Location
    sweden
    Posts
    6
    Rep Power
    0

    Re: Daikin 51e/140

    thx, i will check this first.

  4. #4
    Join Date
    Jan 2022
    Location
    sweden
    Posts
    6
    Rep Power
    0

    Re: Daikin 51e/140

    Hello. I did check the drain lvl sensor and i found a missing bridge connector.
    Now its trowing another fault U0-04. its how does i reset this one?

    best regards

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin 51e/140

    Looks like a refrigerant shortage
    https://www.google.co.uk/url?sa=t&so...QVuC8dmtXCGsV9

  6. #6
    Join Date
    Jan 2022
    Location
    sweden
    Posts
    6
    Rep Power
    0

    Re: Daikin 51e/140

    hi again, thx for input.
    i have checked the instruction manual and here is no U0-04
    The nearst is U4: Wiring error between indoor and outdoor unit. Or indoor and outdoor printed circuit board failure.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin 51e/140

    Look at the top of page 3 of the link I have posted U0-04 Refrigerant Shortage or Blockage

  8. #8
    Join Date
    Jan 2022
    Location
    sweden
    Posts
    6
    Rep Power
    0

    Re: Daikin 51e/140

    hmm.. yes i see
    how to solve this U4 issue, any thoughts?
    it has new cards(pcb) in outdoor and indoor unit.

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin 51e/140

    U4 is a failure of data transmisson between the indoor and outdoor pcbs

    Check the wiring and make sure terminal's 1, 2 and 3 are correctly terminated at each end to rule out mis-wiring. Also check the wiring in any local isolators and high limit switch if you have an indoor condensate pump.

  10. #10
    Join Date
    Jan 2022
    Location
    sweden
    Posts
    6
    Rep Power
    0

    Re: Daikin 51e/140

    thanks ill have to check the wiring this weekand.
    What about U0-04?

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin 51e/140

    Quote Originally Posted by Pirre View Post
    thanks ill have to check the wiring this weekand.
    What about U0-04?
    Unfortunately you will need someone with the correct tools and knowledge to solve that one