    Daikin r32 query



    Daikin split runs on fan only but does not try to start on cool/heat mode when thermostat is set or
    in test run.240v and comms between indoor/outdoor ok,led's on boards all green no sign of damage.U4 comms fault was cleared on controller and no other faults showing.No mobile phone signal i building so could not ring daikin.system is not on a BMS
    Can anyone help?
    Indoor model FCAG100AVEB cassette,outdoor model AZAS100M7V1B on r32 gas 1ph
    SKYAIR ACTIVE SERIES



  2. #2
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Daikin r32 query

    Was it running previously or are you commissioning it?
    Mostly found in the southern part of this green and pleasant land.

  3. #3
    Join Date
    Jan 2015
    Location
    United Kingdom
    Age
    64
    Posts
    37
    Rep Power
    0

    Re: Daikin r32 query

    As far as i know this unit has been running previously.

  4. #4
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Daikin r32 query

    If outdoor won't kick in, check for fluctuating voltage on comms cable, check power to outdoor, check for faults with controller.
    Mostly found in the southern part of this green and pleasant land.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin r32 query

    Is 'Vacuum' mode enabled?

    See page 18 https://www.daikin.be/content/dam/do...de_English.pdf

  6. #6
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Daikin r32 query

    Daikin have had a lot of R32 systems with various errors due to faulty capacitors on the outdoor PCB. I’d give them a call with the model and serial number and see if it in the affected range.

    Edit: I have a photo with the affected range but it’s too big to attach here. Suffice to say your model is affected subject to confirming serial number. I’ve emailed the info to the address on your vCard. 👍

    Further edit: that email bounced back. Send me a message with an alternative email or WhatsApp and I’ll send over.
    Last edited by Tayters; 13-01-2022 at 08:28 PM.

  7. #7
    Join Date
    Jan 2015
    Location
    United Kingdom
    Age
    64
    Posts
    37
    Rep Power
    0

    Re: Daikin r32 query

    Thanks tayters my e-mail is martin.preissler@flakt group.com
    I have heard today that daikin have had problems with boards but it will be really usefull to have this photo.

  8. #8
    Join Date
    Jan 2015
    Location
    United Kingdom
    Age
    64
    Posts
    37
    Rep Power
    0

    Re: Daikin r32 query

    Thanks for reply,voltage is fluctuating from 7-35vdc power 240v acrossphaseon indoor/outdoor unit.how would you check controller as all seems normal.

  9. #9
    Join Date
    Jan 2015
    Location
    United Kingdom
    Age
    64
    Posts
    37
    Rep Power
    0

    Re: Daikin r32 query

    no vacuum mode is not enabled

  10. #10
    Join Date
    Jan 2015
    Location
    United Kingdom
    Age
    64
    Posts
    37
    Rep Power
    0

    Re: Daikin r32 query

    Thanks for everyones help,especially tayters who sent the photo which confirms daikins acknowledgement of the
    outdoor board problem on skyair units