    Hi all,

    I have been asked to offer a cooling system for a freeze dryer. The ice condensor itself will be designed by client.
    But I will give them some advise regarding pipe sizing.

    The system will be a R507A system with DX.
    We aim for -60C in evaporation on coil.
    The coil will be standard AISI 316 pipe bend to a number of hairpins. We will make several pieces in parallel to minimize pressure drop. Around 8 m a piece if possible.

    But this gives quite a big pressure drop unless we go to a big pipe, around 1 1/8". Speed will be 15 m/s which seems ok.

    Question is, how big a pipe do you think we can use and still have liquid touch entire surface of pipe?

    Hope somebody has tried something similar and can come with some input.

    Best regards,
    Peter



  2. #2
    Join Date
    May 2012
    Location
    England
    Age
    59
    Posts
    1,528
    Rep Power
    36

    Re: Freeze dryer, Ice condensor - Pipe dimension

    .

    You say DX so the biggest problem you have there other than pressure drop is
    the length off the single evaporator tube.

    You need to make multiple passes, not one single pass.

    If you had a header you could have three or four passes and that will help with
    liquid surface contact inside the pipe.

    Rob

    .
    .. ... -. .----. - / -- --- .-. ... . / -.-. --- -.. . / --. --- --- -..

  3. #3
    Join Date
    Jan 2022
    Location
    United Arab Emirates
    Posts
    1
    Rep Power
    0

    Re: Freeze dryer, Ice condensor - Pipe dimension

    You need to make multiple passes for kayaks UAE, not one single pass.
    Last edited by caileagany; 15-02-2022 at 07:24 AM. Reason: MORE INFO

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Freeze dryer, Ice condensor - Pipe dimension

    Are you allowed under FGas regulations to manufacturer a new R507 plant in the EU. I thought that was outlawed as of 1 January 2020.