    Daikin VRV II Operation Prohibition



    Hi guys,

    This forum's been really useful previously, so hoping someone will be able to help me out.

    Got an old VRV II system comprising of a RXYQ16M7W1B, RXYQ12M7W1B and a RXYQ10M7W1B.

    The RXYQ10M7W1B is the master - this unit has a failed compressor and we are having absolutely no luck finding spares (I know it's proper old).

    I believe that the master can be placed in to operation prohibition mode, allowing the other two units to operate (albeit at a lesser overall system capacity.)

    I've tried putting it in this mode already (mode 5sec, set x38, return x1, set x1, return x2, mode x1) but it doesn't seem to have any effect.

    Is there any additional configuration needed on any of the 3 units to work in this configuration, or am I chasing the impossible?

    It annoys me that we'll likely need to replace the lot when the two larger units are in working order.

    Cheers,
    Ollie



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin VRV II Operation Prohibition

    You can't lock out the Master.
    Change the Master to 1 of the other units which will make the 10hp unit a slave. Then binary the slave out.

  3. #3
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,044
    Rep Power
    35

    Re: Daikin VRV II Operation Prohibition

    Can you just code out the faulty compressor instead of the whole unit?

  4. #4
    Join Date
    Dec 2021
    Location
    United Kingdom
    Posts
    4
    Rep Power
    0

    Re: Daikin VRV II Operation Prohibition

    Quote Originally Posted by frank View Post
    You can't lock out the Master.
    Change the Master to 1 of the other units which will make the 10hp unit a slave. Then binary the slave out.
    Brilliant - thought the way I was going about it seemed impossible.
    Is that all in the DIP switch states or is there further config needed?

    Cheers,
    Ollie

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Daikin VRV II Operation Prohibition

    Connect the indoor F1F2 circuit wiring to one of the ok units.
    Next connect the other 2 units via Q1Q2 thereby making them slaves
    Then do a full factory reset by pressing and holding the reset button (binary) for 20 seconds on the new Master. Once all indoor handshaking and config is finished you can isolate the failed compressor out by binary in the normal way

  6. #6
    Join Date
    Oct 2013
    Location
    Ukraine
    Posts
    14
    Rep Power
    0

    Re: Daikin VRV II Operation Prohibition

    Master always needs to be largest capacity and closest to the indoors by the refrigerant flow. Is "F1-F2 INDOORS" connected to 10HP unit?

    Quote Originally Posted by frank View Post
    You can't lock out the Master.
    Change the Master to 1 of the other units which will make the 10hp unit a slave. Then binary the slave out.
    Why? Maybe topicstarter makes settings on slave2? 2-38/39/40 can only be changed on master instead of 2-00/19 can be changed on any damaged unit (ever master or slave 1/2).