    Is there an accepted formula to calculate the number of PRV's required in a specific sized freezer room?.
    Derek
    Re: Pressure relief valves for large walk in freezer
    Don't know about calls but this advert has some sizing data which might be of use.
    Click on the 'document download"
    https://www.ixl.co.th/en/products/ac...-relief-ports/
    Croatia
    68
    2,261
    Hi Derek,
    check this link, too
    https://www.fermod.com/valve-2227-cat4-prd342-fp.php
    here you can find info you need .... check download at bottom of the page ...
    Best regards, Josip
    3,362
    Derek,
    Go out the back, you will find some in your warehouse https://www.crh.com.au/products/refr...-relief-valves
    Sep 2008
    Canada
    811
    I just wandering how often people use these PRVs? Personally I didn't see any PRV.
    3,362
    Segei,
    I would call them a vent or port for either way air flow in a cool room or freezer.
    Have heard of implosions on blast freezers.
    Sep 2008
    Canada
    811
    I can’t imagine industrial freezer or blast freezer to have absolutely tight doors. In addition every cold room has evaporator with drain line going outside of that room. I can’t imagine how to get vacuum in industrial cold room.
    3,362
    Segei,
    Understand what you say, but is probably insurance for possible event.
    Client had a -40 blast carton tunnel at abbatoir was turned off for several weeks for maintenance.
    Client turned on with maximum cooling power, room imploded due to rapid contraction of air in refrigerated space.
    Other reasons in link below
    https://www.cold-rite.com.au/post/pr...rooms-freezers