Results 1 to 8 of 8
  1. #1
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14
    Oil jumping in separator
    Hi Everyone
    Hope you are all doing well
    Here is one illusion that oil jumping in oil separator (gea)
    What can be caused?
    Awaiting your kind words.
    Following link
    https://youtube.com/shorts/_lxXlMONXZM?feature=share
    Thanks in advance
  2. #2
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14
    Re: Oil jumping in separator
    I'm trying to upload a video but error occurred everytime
  3. #3
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39
    Quote Originally Posted by shaaf View Post
    Hi Everyone
    What can be caused?
    Following link
    Thanks in advance
    Shaaf,
    Link okay, try running oil level a bit lower, like 25% to 50 % see if better.
    Assume new package.
  4. #4
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19
    Shaaf,
    what is your refrigerant?
  5. #5
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14
    Quote Originally Posted by cricri View Post
    Shaaf,
    NH³ Ammonia
  6. #6
    Join Date
    Nov 2009
    Location
    france
    Age
    64
    Posts
    225
    Rep Power
    19
    Normal oil level should be 1/3 to 1/2 of glass.
    This is not the issue.
    It seems that the is ammonia in the oil, what are disch pressure, disch temperature and oil temp, room temperature?
  7. #7
    Join Date
    Oct 2016
    Location
    Serbia
    Age
    51
    Posts
    110
    Rep Power
    8
    Must be liquid ammonia in oil.
    Nothing to be upset.
    It will be back to normal after some running.
  8. #8
    Join Date
    Jun 2010
    Location
    saudi arab
    Age
    41
    Posts
    82
    Rep Power
    14
    Thanks to everyone
    Problem Sort out.
    Actually it was standby unit we operate it in rare cases. Once Gea engineer PM done and that time he done some settings.
    Oil return from PHE timer setting was changed. It was opening for 30 seconds and delay time was 10 seconds. Instead of oil there was liquid with oil. Liquid was hurting.
    Anyhow good experience
Posting Permissions