Results 1 to 4 of 4
  1. #1
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Temperature drop in liquid line while subcooling



    This is more a theoretical one... we subcool the liquid after condensation...
    Let's say we condense R404A at 45°C and we subcool it further with 15K,..
    then density changes as well and does this mean - theoretically - that pressure will drop as well along this subcooling coil assuming no volume change of the subcooling coil?


    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  2. #2
    Join Date
    Feb 2011
    Location
    scotland
    Posts
    451
    Rep Power
    17

    Re: Temperature drop in liquid line while subcooling

    Is it not a bit of a dynamic system when running. I would think you would have pressure drop due to flow through the pipe as well as from subcooling, but then you also have the vapour/liquid from the upstream keeping it pressurised. If you dont keep it pressurised surely it becomes just saturated liquid.

  3. #3
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Temperature drop in liquid line while subcooling

    Pressure and temperature related for saturated liquid. If subcooled liquid flows in liquid line pressure will drop slightly but it still be subcooled. Subcool temperature can be reduced from 15K to 10K but it still be subcooled.

  4. #4
    Join Date
    Mar 2009
    Location
    U.S.A.
    Posts
    320
    Rep Power
    20

    Re: Temperature drop in liquid line while subcooling

    Fundamental answer: The reduction in volume as you cool the liquid will not change the pressure because the liquid is contained but not enclosed: so the condensing pressure is still pushing on it even though its colder than the condensing temperature. As with any fluid, flow causes a pressure difference and the piping and components downstream of the sub-cooler cannot offer too much resistance or there will be a "new saturation state", that is flashing, in the downstream containment.